One idea runs the whole plant: a fluid changes state at a temperature fixed by its pressure.

24 min read
Intermediate
Auxiliary Machinery & Shipboard Systems
Key Principles at a Glance 5 points
  • A fluid boils or condenses at its saturation temperature, and that temperature varies with pressure. Everything else in refrigeration follows from this one fact.
  • Latent heat is many times larger than sensible heat — which is why a refrigerant circuit moves large quantities of energy for a modest mass flow.
  • The expansion valve causes no energy input or loss, so the points either side of it lie on a line of equal enthalpy.
  • COP falls as condensing temperature rises: a 350 kW plant drops from 4.73 at 25 °C to 3.41 at 35 °C. "Run the condenser as cold as the plant will allow" is an operating rule, not a platitude.
  • High compression ratio costs volumetric efficiency and produces a high discharge temperature — that is the reason for multistage compression and for the low-pressure cut-out setting.

1. Why a Ship Refrigerates

Refrigeration is used on board for two distinct duties:

  • Refrigeration proper — prolong the storage life of perishable cargo and ship's stores by lowering temperature so that metabolic deterioration is prevented.
  • Air conditioning — modify and maintain the condition of air for human comfort.

Both use the same physical process, but the plant, the temperature levels and the control philosophy differ. Refrigeration is a food-safety and cargo-care function; air conditioning is a habitability function.

2. Heat, Enthalpy and Phase Change

The preferred term for heat energy in a liquid or vapour is enthalpy; heat per kilogram is specific enthalpy.

Ice-water-steam phase changes showing sensible heat, latent heat of fusion and vaporisation, and superheat
Figure 1: Ice–water–steam phase changes. The flat sections are the latent-heat (state-change) parts; the sloping sections are sensible heat.

Worked through for 1 kg of ice at −23 °C raised to superheated steam at 200 °C:

StepChangeHeat
1Ice −23 °C → 0 °C (sensible)48.2 kJ
2Ice 0 °C → water 0 °C (latent heat of fusion)333 kJ
3Water 0 °C → 100 °C (sensible, hf = 419.1 kJ)419.1 kJ
4Water 100 °C → steam 100 °C (latent heat of vaporisation, hfg)2256.7 kJ
5Steam 100 °C → 200 °C (superheat)299.2 kJ
6Water 0 °C → dry saturated steam at 100 °C (hg)2675.8 kJ

The engineer's take-away: steps 2 and 4 do the work. Step 4 — the latent heat of vaporisation — is the one the evaporator lives on, and step 2's equivalent on the condenser side is where the heat is thrown away. Latent heat is many times larger than sensible heat, which is why a refrigerant circuit moves large quantities of energy for a modest mass flow.

For a substance with constant specific heat capacity, sensible heat is Q = m · cp · (θ₂ − θ₁).

Datum note

The datum for water is taken as 0 °C because that is where the state change occurs. For refrigerants the datum is often taken at −40 °C. This has no physical significance — it just avoids a mass of negative numbers.

3. Saturation Temperature — the Single Most Important Idea

The temperature at which a fluid boils or condenses is known as the saturation temperature, and it varies with pressure.

Everything else follows from this:

  • Raise the pressure of a vapour → its saturation temperature rises.
  • Lower the pressure of a liquid → its saturation temperature falls.
Saturation curve showing evaporation and condensation of a fluid at two pressures
Figure 2: Evaporation at the low pressure Pe / Te and condensation at the high pressure Pc / Tc.

So the job of the four main components is simply to make a fluid boil at a low temperature (so it absorbs heat from the cold space) and condense at a high temperature (so it rejects heat to sea water or air):

1. Compressor

Raises the pressure of the vaporised refrigerant, so raising its saturation temperature above that of the sea water or air cooling the condenser. It also promotes circulation of the refrigerant by pumping it round the system.

2. Condenser

The refrigerant is liquefied and subcooled below the saturation temperature by the circulating sea water or air. The latent heat originally taken in at the evaporator is thus transferred to the cooling medium.

3. Expansion valve

The regulator through which refrigerant flows from the high-pressure side to the low-pressure side. The pressure drop causes the saturation temperature to fall below the actual temperature, so some liquid flashes off, taking latent heat from the remainder and cooling it. It also maintains the pressure difference between condenser and evaporator and meters refrigerant to the evaporator at the correct rate.

4. Evaporator

Refrigerant entering at a temperature lower than the secondary coolant (air or brine) receives latent heat and evaporates.

SATURATION TEMPERATURE FOLLOWS PRESSURE compressor raises pressure LOW PRESSURE — evaporator P_e / T_e refrigerant boils cold absorbs latent heat from the space HIGH PRESSURE — condenser P_c / T_c refrigerant condenses hot rejects latent heat to sea water Raise the pressure of a vapour and its saturation temperature rises. Lower the pressure of a liquid and its saturation temperature falls. That single fact is why a compressor can make a fluid boil at −30 °C and condense at +35 °C.
Critical temperature

The temperature above which a gas cannot be liquefied by isothermal compression, however hard it is compressed. Every refrigerant must have its critical temperature comfortably above the normal condensing temperature. CO₂ is the classic offender: critical temperature 31 °C, so once the sea water reaches about 23 °C (31 °C less an 8 °C differential) the critical point has been reached and the efficiency of the plant steadily decreases.

4. The Vapour Compression Cycle

Simple fridge system with compressor, condenser, expansion valve and evaporator
Figure 3: Simple fridge system — the four essential components and nothing else.

A liquid boils and condenses at a temperature which depends on its pressure. In boiling it must obtain the latent heat of evaporation; in condensing the latent heat must be given up again. The basic refrigeration cycle makes use of the boiling and condensing of a working fluid at different temperatures and therefore at different pressures.

Basic refrigeration cycle for R.22 evaporating at -5 C and condensing at 35 C
Figure 4: Basic refrigeration cycle, R.22. Evaporating −5 °C at 3.21 bar; condensing 35 °C at 12.54 bar.

Worked example from the figure — a typical R.22 circuit:

91.4
kJ/kg entering evaporator
249.9
kJ/kg saturated gas leaving
158.5
kJ/kg cooling effect

A working system needs a connection between the condenser and the inlet to the evaporator to complete the circuit. Since these are at different pressures, this connection requires a pressure-reducing and metering valve. Because the reduction in pressure at this valve must cause a corresponding drop in temperature, some of the fluid flashes off into vapour to remove the energy for this cooling. The volume of working fluid therefore increases at the valve by this amount of flash gas — which gives rise to the name expansion valve.

Complete basic cycle showing suction, discharge, high-pressure liquid and low-pressure liquid plus flash gas
Figure 5: Complete basic cycle — high-pressure gas → condenser → high-pressure liquid → expansion valve → low-pressure liquid + flash gas → evaporator → low-pressure gas (suction).

The four process steps in order, as they will be described in an oral:

1

Evaporation at low pressure/temperature — absorbs latent heat from the load.

2

Compression — raises pressure and saturation temperature.

3

Condensation at high pressure/temperature — rejects superheat, then latent heat, then a little subcooling, to sea water or air.

4

Expansion — throttles back to evaporator pressure; flash gas cools the remaining liquid.

5. Coefficient of Performance

Since the vapour compression cycle uses energy to move energy, the ratio of the two is a direct measure of performance. This ratio — the coefficient of performance (COP) — was first expressed by Sadi Carnot in 1824 for an ideal reversible cycle, based on the two temperatures of the system and assuming all heat is transferred at constant temperature.

Ideal reversed Carnot cycle
Figure 6: Ideal reversed Carnot cycle.
COP = 1 / [(Tc / Te) − 1]

For the −5 °C / 35 °C case (268.15 K / 308.15 K):

COP = 1 / [(308.15 / 268.15) − 1] = 6.7

Because there are mechanical and thermal losses in a real circuit, the actual COP is always less than the ideal Carnot figure. For practical purposes it is the ratio of the cooling effect to the input compressor power.

Transfer of heat through the walls of the evaporator and condenser requires a temperature difference. With a 5 K difference on each, the fluid operating temperatures become 263.15 K and 313.15 K and the COP falls to 5.26.

Modified reversed Carnot cycle with 5 K temperature differences
Figure 7: Modified reversed Carnot cycle, ΔT = 5 K on both exchangers. COP falls from 6.7 to 5.26.

Effect of exchanger size — worth memorising

ChangeEffect 1Effect 2
Larger evaporatorHigher suction pressure → denser gas entering the compressor → greater mass of gas for a given swept volume → higher refrigerating dutyHigher suction pressure → lower compression ratio → less power for a given duty
Larger condenserLower condensing temperature → colder liquid entering the expansion valve → more cooling effectLower discharge pressure → lower compression ratio → less power

The practical COP / condensing-temperature trade (a favourite oral)

A 350 kW air-conditioning plant:

Condensing temperatureCOPWeekly electricity cost
35 °C (summer maximum)3.41256
30 °C4.00219
25 °C (probable minimum)4.73184
Why this matters at sea

This is why "run the condenser as cold as the plant will allow" is a real operating rule, not a platitude. It is also why the condenser pressure regulator should be set at the lowest pressure that gives satisfactory operation, and why a dirty condenser costs money.

6. Reading the Pressure–Enthalpy (Mollier) Chart

Once basic theory is established on T–s charts, the emphasis in practice shifts to the p–h (Mollier) chart, because heat extracted, heat rejected and the work-done heat equivalent can all be read off directly from the h axis in kJ/kg.

Pressure-enthalpy diagram showing subcooled liquid, liquid plus vapour, and vapour regions
Figure 8: Pressure–enthalpy diagram. A fluid being heated passes from subcooled (a) → boiling point (b) → fully evaporated (c) → superheated (d).
Mollier diagram with the refrigeration cycle ABCD plotted
Figure 9: p–h or Mollier diagram with the refrigeration cycle ABCD drawn on it.
p-v and p-h diagrams of the refrigeration cycle
Figure 10: p–v diagram (shown only for comparison with other cycles; rarely used in refrigeration) and the p–h diagram.
The vapour compression system with the cycle points marked
Figure 11: The vapour compression system, with the cycle states identified.

How to read the cycle:

  • A→B, compression. Taken as adiabatic (isentropic) for calculation work — a vertical line. In reality it alters according to compressor type and is never perfectly vertical.
  • B→C, condensation. The condenser receives high-pressure superheated gas, cools it to saturation temperature, condenses it to liquid, then subcools it slightly. The energy removed is the refrigerating effect PLUS the heat of compression.
  • C→D, expansion. There is no energy input or loss within the expansion valve, so C and D lie on a line of equal enthalpy.
  • D→A, evaporation. The distance D to the saturated-vapour curve indicates the proportion of flash gas at that point.

In a working circuit, the vapour leaving the evaporator will be slightly superheated (point A moves to A1) and the liquid leaving the condenser subcooled (C moves to C1). Pressure losses also occur across the gas inlet and outlet and through the heat exchangers and piping. Taking all this into account, the refrigerating effect (A1 − D1) and the compressor energy (B1 − A1) can be read off directly in kJ/kg.

Undercooling before the expansion valve reduces flash-off after the throttle, so lowering the quality and increasing the refrigerating effect in the evaporator. The practical flash-off loss is about 20 % of refrigerating effect for Freon, which does not justify the complexity of fitting two expansion valves with an intermediate liquid valve between them.

COP = heat energy received / heat energy equivalent of work done

For Freon this is approximately 4.7.

7. Volumetric Efficiency

In a reciprocating compressor there is always a small clearance space at the top of the stroke, arising from gas ports, manufacturing tolerances, and an allowance for thermal expansion and contraction in operation. High-pressure gas left in this space at the end of the discharge stroke must re-expand to suction pressure before a fresh charge of gas can be drawn in.

Volumetric efficiency against pressure ratio for R.22 with 7 percent clearance
Figure 12: Volumetric efficiency vs pressure ratio, R.22 with 7 % clearance. Falls away steeply above about 5:1.
  • Clearance space is usually 4–7 % of swept volume; it is possible to design compressors with less.
  • The loss of useful working stroke increases with the ratio of suction to discharge absolute pressures, so compressor efficiency falls off.
  • Reed's adds the practical limit: all reciprocating compressors should have the minimum reasonable piston clearance, 1.5 mm maximum, so as to give maximum efficiency.
Reciprocating compressor indicator diagram showing clearance volume and re-expansion
Figure 13: Indicator diagram — Pc, Pe, clearance volume, re-expansion, compression.
The link to protection settings

This is the reason for multistage compression and for the low-pressure cut-out setting. A high compression ratio costs volumetric efficiency and produces a high discharge temperature.

8. Multistage Cycles

Where the ratio of suction to discharge pressure is high enough to cause a serious drop in volumetric efficiency or an unacceptably high discharge temperature, vapour compression must be carried out in two or more stages. Two basic systems are used.

Compound system

Uses the same refrigerant throughout a common circuit, compressing in two or more stages. Discharge gas from the first stage is too hot to pass directly to the high-stage compressor, so it is cooled in an intercooler, using some of the available refrigerant from the condenser. The opportunity is also taken to subcool the liquid passing to the evaporator. Small compound systems may cool the interstage gas by direct injection of liquid refrigerant into the pipe.

Compound cycle circuit and Mollier diagram
Figure 14: Compound cycle. Low-stage compressor → intercooler → high-stage compressor.

Reed's describes the same arrangement in shipboard terms: an 8-cylinder unit can operate single-stage down to −20 °C, and for temperatures below this, 6 cylinders perform the initial compression and the remaining 2 cylinders perform the final compression, with special changeover valves.

Cascade system

Two separate refrigeration systems, one acting as a condenser to the other. This permits the use of different refrigerants in the two systems; high-pressure refrigerants such as R.13 are common in the lower stage.

Cascade cycle circuits and Mollier diagram
Figure 15: Cascade cycle — low-temperature system and high-temperature system coupled through the inter-stage condenser.
Caution when reading the charts

The Mollier diagrams for compound and cascade systems indicate the enthalpy change per kilogram of circulated refrigerant, but the mass flows are different for the low and high stages. Do not add them naively.

9. Alternative Cycles — Know Them, But Know They Are Alternatives

Absorption cycle

Vapour is withdrawn from an evaporator by absorption into a liquid. Two combinations are in use: ammonia gas into water, and water vapour into lithium bromide (non-toxic, so used for air conditioning — but restricted to systems above the freezing point of water).

Absorption cycle basic circuit and circuit with heat interchange
Figure 16: Absorption cycle. (a) Basic circuit. (b) Circuit with heat interchange between the two liquor paths.

Refrigerant vapour from the evaporator is drawn into the absorber by the liquid absorbent, which is sprayed into the chamber. The resulting solution (liquor) is pumped up to condenser pressure and the vapour is driven off in the generator by direct heating. The high-pressure refrigerant gas given off is condensed in the usual way and passed back through the expansion valve into the evaporator. Weak liquor from the generator passes through another pressure-reducing valve to the absorber. Overall thermal efficiency is improved by a heat exchanger between the two liquor paths and a suction-to-liquid heat exchanger for the refrigerant. Power to the liquor pump is usually electric, but the heat to the generator may be any form of low-grade energy — oil, gas, hot water or steam (solar radiation can also be used).

The overall energy used is greater than with the compression cycle, so the COP is lower:

Per 100 kW cooling at 3 °C evaporation, 42 °C condensationAbsorptionVapour compression
Load100.0100.0
Pump / compressor (electricity)0.130.0
Low-grade heat165
Heat rejected265.1130.0

The absorption system is used to advantage where there is a cheap source of low-grade heat or where there are severe limits on electrical power available.

Reed's describes the domestic absorption unit in detail — the hydrogen/ammonia/water system with no moving parts, continuous in operation when provided with a heat source such as a town gas burner or electric element. Total pressure (sum of partial pressures) is constant through the system. It requires no compressor or pump, and is silent and vibrationless. It is fairly often used in domestic units ashore but rarely on board ship, because the correct and steady level is critical for correct working.

Absorption type refrigeration unit
Figure 17: Absorption type refrigeration unit (hydrogen/ammonia/water, no moving parts).

Steam ejector system

The low pressures (8–22 mbar) required to evaporate water as a refrigerant at 4–7 °C for air-conditioning duty can be obtained with a steam ejector; high-pressure steam at 10 bar is commonly used. The COP is somewhat less than with the absorption system, so its use is restricted to applications where large volumes of steam are available when required (large, steam-driven ships) or where water is to be removed along with cooling, as in freeze-drying and fruit juice concentration.

Air cycle

Any gas, when compressed, rises in temperature; conversely, if it is made to do work while expanding, the temperature drops. Use is made of the sensible heat only. The main application is the air-conditioning and pressurisation of aircraft. The turbines turn at very high speeds to obtain the necessary pressure ratios and are consequently noisy. The COP is lower than with other systems. The normal cycle uses the expansion of the air to drive the first stage of compression, so reclaiming some of the input energy.

Air cycle cooling: compressor, heat exchanger, expander, cold air to process
Figure 18: Air cycle cooling — compressor → heat exchanger → expander → cold air to process.

Thermoelectric (Peltier) cooling

Passage of an electric current through junctions of dissimilar metals causes a fall in temperature at one junction and a rise at the other — the Peltier effect. Improvements have been made possible by suitable semiconductors. Applications are limited in size owing to the high electric currents required; practical uses are small cooling systems for military, aerospace and laboratory use.

Thermoelectric cooling with P and N type semiconductors
Figure 19: Thermoelectric cooling, P and N type elements.

Total-loss refrigerants

Some volatile fluids are used once only and then escape to atmosphere. Two are in general use:

  • Carbon dioxide — stored as liquid under pressure and low temperature, released when cooling is required. Below its critical point at atmospheric pressure, so it can only exist as "snow" or a gas. Released at −78.4 °C.
  • Nitrogen — released at −198.8 °C.
  • Water ice can also be classified as a total-loss refrigerant.

Since both gases come from the atmosphere, there is no pollution hazard.

10. Requirements for a Working Fluid

Ten requirements for a refrigerant in a vapour compression cycle:

1

A high latent heat of vaporisation

2

High density of suction gas

3

Non-corrosive, non-toxic and non-flammable

4

Critical temperature and triple point outside the working range

5

Compatibility with materials of construction, with lubricating oils, and with other materials present in the system

6

Convenient working pressures — not too high, and preferably not below atmospheric

7

High dielectric strength (for compressors having integral electric motors)

8

Low cost

9

Ease of leak detection

10

Environmentally friendly

No perfect fluid exists

No single working fluid has all these properties. The present situation has been dominated by the need for environmentally friendly fluids.