Deck Foam & Inert Gas (IG) Systems on Tankers
Foam blanket types and deck-foam rates plus inert gas — flammability limits, scrubber, blowers, deck seal and working flow.
Key Principles at a Glance 7 points
- Foam is an aggregate of air-filled bubbles from aqueous solution, lower in density than the lightest flammable liquid, forming a coherent floating blanket that excludes air, cools fuel, suppresses vapour against re-ignition, adheres to surfaces and fills cavities — but foam solutions conduct electricity and are not for electrical fires.
- Foam concentrates are protein at 3–6% for crude oil, fluoroprotein at 3–6% with a vapour-sealing film for crude or refined oils, special alcohol-type with an insoluble barrier for chemicals, and synthetic AFFF plus medium/high-expansion at 20:1 to 1000:1 for local and engine-room use.
- SOLAS requires fixed deck foam on ships carrying chemicals or oils in bulk, larger on IMO type-2 and type-3 chemical tankers: oil 0.6 L/m²/min over the whole deck or 6.0 over the largest tank, chemical 2.0 over the whole deck or 20.0 over the largest tank.
- The deck-foam plant is water supply plus foam-liquid storage with vent, gauge and manhole, automatic 3–6% proportioner fed 10 m head above water pressure by an electric pump, deck main with isolating valves, monitors on normally-closed butterfly valves and four 400 L/min branches.
- Gas mixtures burn only between LFL (leanest) and UFL (richest): below LFL too lean and above UFL too rich will not burn; higher temperature lowers LFL and raises UFL while greater pressure raises both.
- Flue-gas IG is scrubbed boiler uptake gas at 4–5% oxygen; tanks are held inert at 8% oxygen or less under 100 mmwg positive pressure, with blowers at 125% plus standby, GRP scrubber with venturi/filter/spray, epoxy P/V breaker, PLC touchscreen in the CCR and O2 analyser venting above 8%.
- Working flow runs uptake valve → scrubber → overboard/bilge drains → demister → blowers → O2 analyser → deck seal → tanks with P/V valves; theory allows 11.5% oxygen but practice holds 8%; gas freeing replaces IG with fresh air while purging introduces IG to cut O2 and HC; replacement is by dilution or displacement.
1. Foam Principle & Blanket Action
For "explain deck foam for fire fighting?" (Q25), start with what foam is and what the blanket does. Foam for fire protection is an aggregate of air-filled bubbles formed from aqueous solutions, and is lower in density than the lightest flammable liquids.
1. Air Exclusion & Smothering
Forms a coherent floating blanket over burning hydrocarbons, creating a physical barrier that cuts off atmospheric oxygen supply to the flame front.
2. Fuel Cooling & Steam Quenching
The water content draining from the bubble matrix cools the liquid fuel below its flashpoint; vaporised drainage water expands into steam to displace oxygen locally.
3. Vapour Suppression & Re-Ignition Barrier
The stable blanket traps volatile hydrocarbon gases beneath the foam surface, preventing flammable vapour from mixing with air even after the fire is out.
4. Surface Adherence & Progressive Attack
Adheres to hot vertical tank bulkheads and pipework, providing radiant heat shielding and allowing firefighters to advance foam coverage progressively across the deck.
Because foam solutions consist of salt or fresh water with electrolyte concentrate additives, foam is electrically conductive and strictly prohibited for use on energized switchboards or electrical machinery.
2. Foam Concentrate Types
The principal use of foam is to extinguish burning flammable or combustible liquid spills or tank fires by developing a coherent coolant blanket. Give the four concentrate families with dilution and duty:
Protein Foam Concentrate
Formulated from natural animal protein hydrolysate. Mixed at 3% to 6% with sea/fresh water. Produces a stiff, dense, cohesive blanket with exceptional burnback resistance. Used primarily on crude oil tank fires.
Fluoroprotein Foam Concentrate
Enhanced with synthetic fluorochemical surfactants. Mixed at 3% to 6%. Deposits an ultra-thin vaporisation-preventing film over the fuel surface, resisting fuel contamination and shed fuel pickup. Used on crude oil and refined petroleum products.
Alcohol-Resistant (AR) Concentrate
Contains hydrophilic polysaccharide polymers. When applied to water-miscible polar solvents (alcohols, ketones, esters), it precipitates an insoluble polymeric membrane barrier that stops chemical breakdown of the bubble wall. Mandatory for chemical tankers.
Synthetic AFFF & High-Expansion
Aqueous Film Forming Foam (AFFF) spreads rapidly across fuel spills for rapid flame knockdown. High-expansion foam generators produce expansion ratios from 20:1 up to 1000:1, designed for total volumetric flooding of engine rooms and pump rooms.
Protein = crude at 3–6% • Fluoroprotein = film on crude and refined at 3–6% • Alcohol-type = insoluble barrier for chemicals • Synthetic = AFFF, hi-ex 20:1–1000:1 for local and engine-room use.
3. Deck Foam Regulation, Rates & Components
SOLAS/IMO regulation: for ships carrying chemicals or oils in bulk, a fixed deck-foam system for extinguishing fires on deck or in tanks is required. The systems are identical in principle, but for chemical tankers of IMO type 2 and 3 the foam system is considerably larger than for crude-oil tankers, due to the higher fire risk of chemicals.
System description (components):
1. Water Supply
Dedicated sea-water supply provided by the ship's fire pumps, delivering pressurized water continuously to the foam proportioning station.
2. Foam-Liquid Storage Tank
Stainless steel or epoxy-lined atmospheric tank complete with air vent, level sight glass, pressure vacuum valve, and access manhole.
3. Proportioning Device & Pump
High-pressure electric positive-displacement pump delivering concentrate to the automatic balanced proportioner at 3% to 6%, maintaining a minimum 10 m head pressure above inlet water pressure under all flow conditions.
4. Deck Monitors & Handlines
Deck main equipped with sectional isolating valves. Deck foam monitors isolated by normally-closed butterfly valves, plus four portable foam branchpipes (each 400 L/min solution rate).
Oil 0.6 / 6.0 — chemical roughly three times richer at 2.0 / 20.0. Always quote whole-deck first, largest-tank second; proportioner 3–6% with 10 m head margin.
4. Inert Gas: Flammable Limits & Definitions
For "explain the IG system?" (Q26), start with flammable limits, the Coward flammability relationship, and board operational definitions:
Lower Flammable Limit (LFL)
The leanest combustible mixture capable of propagating flame. For petroleum hydrocarbon vapors in air, LFL is approximately 1.0% by volume. Below LFL, the mixture has insufficient fuel to burn (too lean).
Upper Flammable Limit (UFL)
The richest combustible mixture capable of propagating flame. For petroleum vapors in air, UFL is approximately 10.0% – 11.0% by volume. Above UFL, there is insufficient oxygen to sustain combustion (too rich).
Temperature & Pressure Influence
Rising temperature widens the flammable band (lowers LFL and raises UFL). Higher absolute pressure increases both LFL and UFL, expanding the explosive envelope under compression.
Purging vs. Gas Freeing
Purging: introducing IG into an inert tank to reduce hydrocarbon concentration to ≤ 2% before air admission, preventing entry into the flammable zone. Gas freeing: replacing inert gas with breathable fresh air (21% O²).
5. IG Plant Construction Parts
Surveyors expect the major plant assemblies to be recited in the exact sequence the gas encounters them from uptake to weather deck:
1. Boiler Uptake Valve
Controls hot gas take-off from boiler exhaust. Manufactured from heat-resistant cast steel. Fitted with compressed-air sealing to prevent exhaust gas entering the idle plant, plus steam/air soot blowers to clear carbon fouling.
2. Flue Gas Scrubber Tower
Three-stage cooling and cleaning tower internally lined with acid-resistant GRP (glass-reinforced plastic). Features a venturi quencher, impingement wet filter plates, and sea-water spray nozzles. Strips > 90% of SO² and soot, draining effluent overboard via an acidic U-seal.
3. Centrifugal IG Blowers
Two single-stage centrifugal blowers (1 duty + 1 standby) on resilient anti-vibration mountings. Minimum aggregate capacity is 125% of the ship's maximum cargo discharge rate, ensuring positive line pressure under peak discharge.
4. Continuous O² Analyser
Dual paramagnetic or zirconium sensor cells sampling gas post-blower. If oxygen content rises above 8% by volume, it instantly triggers an audible/visual alarm, opens the 3-way atmospheric vent valve, and trips the deck main shut-off valve.
5. Deck Water Seal
The principal barrier separating the hazardous cargo tank deck from the non-hazardous machinery space. Liquid column physically blocks hydrocarbon reverse flow. Equipped with a demister pad and a mandatory low-water-level alarm.
6. Liquid P/V Breaker
Epoxy-coated safety breaker located on the weather deck, filled with a water-glycol mixture. Protects cargo tanks against severe over-pressure or deep vacuum in the event of mechanical high-velocity P/V valve failure.
6. IG Working Flow, Oxygen & Gas Replacement
For "trace the inert gas from boiler uptake to cargo tank", explain the process as ordered engineering stages with operational parameters:
Gas Replacement Principles (Viva Question):
Dilution Method (Turbulent Mixing)
Inert gas is injected at high velocity from deck level, penetrating to the tank bottom. It mixes turbulently with existing vapors, and the homogeneous mixture is continuously expelled from top vents. Requires approximately 3 to 4 tank volumes of IG to achieve safe levels.
Displacement Method (Piston Layering)
Utilises density differences. Cool, dense inert gas enters the tank top at low velocity, settling to the bottom like a piston and lifting the lighter, warmer hydrocarbon vapors upward and out through the bottom purge pipe. Highly efficient, requiring only 1.2 to 1.5 tank volumes.
Deliver the process in surveyor cadence: Boiler Uptake → Scrubber → Demister → Blowers (125%) → O² Analyser (Dump > 8%) → Deck Water Seal → Deck Isolating Valve → Cargo Tanks (+100 mmwg) guarded by Liquid P/V Breaker.
7. Foam & IG Oral-Exam Recap
Surveyors frequently pair fixed deck foam (Q25) and inert gas systems (Q26) in a single high-intensity oral exam segment. Master the exact operational numbers and system schematics below:
| Vessel / System | Whole Deck Rate | Largest Tank Rate | Regulatory Basis |
|---|---|---|---|
| Oil Tanker Deck Foam | 0.6 L/m²/min | 6.0 L/m²/min | SOLAS II-2 Reg 10.8 • 20 min discharge |
| Chemical Tanker Deck Foam | 2.0 L/m²/min | 20.0 L/m²/min | IBC Code Chapter 11 • Alcohol-resistant foam |
| Foam Proportioner Pump | +10 m head (~1.0 bar) above water inlet pressure | Positive displacement • 3% to 6% automatic | |
| Inert Gas Oxygen Level | ≤ 5% O² at Blower | ≤ 8% O² in Cargo Tanks | SOLAS II-2 Reg 4.5.5 • 11.5% theoretical stop |
| Fixed IG Carriage (from 1 Jan 2016) | All tankers ≥ 8,000 DWT (previously ≥ 20,000 DWT) | SOLAS II-2 Reg 4.5.5 as amended | |