Back to Fire Safety
Safety

CO2 Fixed Fire-Fighting System on Ships

The CO2 fixed system end to end: bottles and regulations, the CO2 room and safeties, quantity calculation and maintenance, and engine-room and purifier fire actions.

12 min read
Advanced
Safety
Key Principles at a Glance 6 points
  • CO2 extinguishes by smothering plus cooling, bringing oxygen below 15 percent; category-A machinery spaces of 500 cu m and above need a fixed system that puts 85 percent of the charge in within 2 minutes.
  • Bottles are drawn steel hydro-tested to 228 bar, stowed below 55 °C at about 52 bar, checked by level, radio-isotope or weighing, each with a syphon tube and a bursting disc set for 177 bar at 63 °C.
  • The CO2 room is for sole use, not more than one deck below the open deck with stair or ladder access, 6 air changes per hour, outward-opening gas-tight doors, below 55 °C, 2.4 m headroom — and aft of the collision bulkhead if sited outside machinery spaces.
  • System safeties run from the cabinet trip switch through master valve, manifold relief, bottle safety pins, non-return check valve and the 4-bar leak alarm with its cooler-bottle hunt procedure, piped in mild steel galvanised with insulated, ventilated, gas-tight room boundaries.
  • Quantities are 30 percent of the largest cargo space, 40 percent of the largest machinery space excluding casing (35 percent including casing), using volume-times-factor over 0.56 (cu m per kg at 21.1 °C and 1 bar) over 45.4 kg per cylinder — the worked vessel needs 212 bottles at 58 bar, 120 kg charge with 72–80 tare, 120 s design against 107 s actual.
  • Engine-room fire action is alarm, muster, headcount, ventilation stops, fuel stops, boundary cooling and CO2 release; purifier-room action adds stopping the purifier from outside, shutting purifier ventilation, flaps and fuel QCV, with prevention by double-sheathed pipes, drip trays, anti-spill tape, mist plus CO2, quick-closing valves with remote stops, and detection.

1. Principle, Regulation & CO2 Bottles

This is the most important section in the Safety oral — surveyors ask at least one main question from CO2, and a weak answer here fails the sitting. For "what is the principle of CO2 flooding?"smothering plus cooling, reducing the oxygen content to below 15 percent so combustion cannot sustain. The system works only inside enclosed spaces — in open space it does not work at all — so it protects machinery spaces, engine rooms, purifier rooms and cargo holds.

  • Regulation: SOLAS requires that a ship with a category-A machinery space of 500 cu m and above volume be fitted with an additional fixed fire-fighting system.
  • Discharge rule: 85 percent of the required CO2 quantity must be released into the space within 2 minutes of actuating the system — and of evacuating the fire-affected space.
  • Operation authority: the system must be operated by the Chief Engineer or Second Engineer — those two are responsible for the whole release operation.

CO2 bottles — construction and fittings:

  • Bottles are solid drawn steel, hydraulically tested to 228 bar.
  • Bottles must not be stored where the temperature exceeds 55 °C; bottle pressure is normally about 52 bar and varies with temperature.
  • Contents are checked by level indicator, radio-active isotope gun, or weighing.
  • In each bottle head assembly the bursting disc is designed to rupture at 177 bar produced by a temperature of about 63 °C.
  • Each bottle has a syphon tube so that liquid CO2 is discharged from the bottle.

Why the syphon tube matters — say this line:

  • Without the syphon tube the CO2 would evaporate from the surface, giving a very slow discharge rate and, by taking its latent heat, would cause the remaining CO2 in the bottle to freeze.
  • Liquid discharge at the nozzle flashes to gas — that flash gives the cooling half of the principle alongside smothering.
Why the Syphon Tube?

Liquid CO2 sits at the bottom and flashes to gas at the nozzle — that flash gives the cooling half of the principle. A bottle without its dip tube blows vapour only, so always confirm syphon tube + bursting disc 177 bar at 63 °C in one breath.

LIQUID CO2 45.4 kg @ 52 bar CO2 Gas Vapor 177 bar MANIFOLD Quick-Release Actuating Lever + Mechanical Safety Pin Safety Bursting Disc: 177 bar at 63 °C ambient Non-Return Check Valve (Prevents partial-release backflow) Full-Length Siphon Tube (Evacuates liquid CO2 first for flash cooling) Solid Drawn Seamless Steel: 228 bar hydro test, tare 72–80 kg SOLAS FLOODING CRITERIA • Discharges 85% of gas within 2 minutes • Dilutes ambient oxygen level to below 15% • Liquid flashing absorbs latent heat for heavy cooling
Figure 1: Standard 45.4 kg marine CO2 cylinder cutaway — solid drawn steel shell tested to 228 bar, siphon dip tube for liquid discharge, bursting disc (177 bar / 63 °C), and non-return manifold isolation valve.
45 kg CO2 cylinder spec with siphon tube, valve and pressures
Reference sketch (course notes): the 45 kg cylinder spec — siphon tube, valve, test and bursting pressures. Source: Kunjal Shah Part 2 — Fire Fighting Appliances.
CO2 bottle head with valve, levers and pilot tubing
Reference photo (course notes): the bottle head in the flesh — valve, levers and pilot tubing. Source: Kunjal Shah Part 2 — Fire Fighting Appliances.
CO2 manifold valve with brass bursting disc
Reference photo (course notes): the manifold valve with its brass bursting disc. Source: Kunjal Shah Part 2 — Fire Fighting Appliances.

2. CO2 Room, Safeties & Leak Hunting

For "describe your CO2 room" (Q21c), give the room first, then the safety chain, then the leak drill:

CO2 room regulation (Q21c):

  • The storage room shall be used for no other purposes.
  • If below deck, it shall be no more than one deck below the open deck and directly accessible by stairway or ladder from the open deck.
  • Spaces below deck, or without open-deck access, shall have mechanical ventilation taking exhaust from the bottom of the space, sized for at least 6 air changes per hour.
  • Access doors open outwards, and bulkheads, decks, doors and every closing means forming boundaries with adjacent enclosed spaces shall be gas tight.
  • Room temperature maintained below 55 °C.
  • Minimum clear height 2.4 m for manifold mounting and cylinder weighing.
  • If the fixed medium is stored outside a protected space, it shall sit in a room behind (aft of) the forward collision bulkhead.

System safeties (Q21b) — walk the chain in order:

  • Trip switch: the control cabinet has a special trip switch for ventilation trip and CO2 alarm — as soon as you open the cabinet it trips ventilation and sounds the alarm.
  • Master valve (Q21d): fitted on the main manifold line going to machinery or cargo spaces — it prevents CO2 reaching any space on an accidental release; open it only as part of the ordered release sequence.
  • Relief valve: located at the end of the manifold — if manifold pressure exceeds the set point it lifts to atmosphere at 180 bar.
  • Safety pin: provided in each bottle head assembly — it locks the operating lever against accidental operation; pull it out for manual operation.
  • Bursting disc: also in each bottle head assembly — bursts when bottle pressure exceeds 177 bar with about 63 °C around the bottle.
  • Non-return check valve: located between each bottle and the manifold — acts as a non-return so that blow-through service air cannot pass back, and on a partial release (a few bottles for a cargo hold) the pressurised manifold cannot force open the unoperated bottles after the pilot cylinder fires.
  • CO2 leak alarm: located on the manifold, working as a pressure switch at 4 bar. Any leaking bottle feeds gas into the manifold; at 4 bar it trips the alarm. Since even a small leak off a 52-bar bottle pressurises the manifold fast, the alarm tells you a bottle leaks — but never which one. Finding it: two persons go together with communication equipment, ventilate the room and wait outside until gas-free, then enter and hand-touch bottles in turn — the leaking bottle is markedly cooler than its neighbours. Mark every cooler bottle, check all of them, and report the count.
  • Pipework: solid drawn mild steel, galvanised against corrosion.
RELEASE CABINET M Door Microswitch (Trips Fans & Sounds Alarm) PILOT 1 PILOT 2 1. OPEN MASTER VALVE 2. FIRE PILOT TO BANK Pilot Gas Line MAIN CYLINDER BANK (200+ BOTTLES) MAIN COLLECTOR MANIFOLD 4 bar Leak Alarm 180 bar Relief to Deck DISTRIBUTION MASTER VALVE (Pneumatic / Manual) Engine Room Bilge & Tops Purifier Room (7 Cylinders) Cargo Holds (Selective) Discharge Horns
Figure 2: High-Pressure CO2 Fixed Firefighting installation schematic — remote cabinet microswitch (ventilation trip & pre-discharge alarm), dual pilot cylinders, main cylinder bank with non-return check valves, 4-bar manifold leak alarm, 180-bar relief valve, and master distribution valve.
Fixed CO2 system sketch with pilot bottles, manifold and nozzles
Reference sketch (course notes): the whole fixed system on one page — pilot bottles, manifold, master valve and nozzle branches. Source: Kunjal Shah Part 2 — Fire Fighting Appliances.
CO2 bottle room with banked cylinders and pipework
Reference photo (course notes): the bottle room — banked cylinders, racks and pipework. Source: Kunjal Shah Part 2 — Fire Fighting Appliances.
CO2 manifold gauge
Reference photo (course notes): the manifold gauge surveyors tap and read. Source: Kunjal Shah Part 2 — Fire Fighting Appliances.
CO2 cabinet alarm circuit sketch with door switch and sounder
Reference sketch (course notes): the cabinet alarm circuit — door switch, ventilation cutout and sounder loop. Source: Kunjal Shah Part 2 — Fire Fighting Appliances.
CO2 leakage alarm switch and gauge at 4 bar
Reference photo (course notes): the 4-bar leakage alarm switch and gauge. Source: Kunjal Shah Part 2 — Fire Fighting Appliances.
1
Cabinet Access & Automatic Safety Interlock

Break glass, unlock remote release cabinet door. The integrated microswitch trips mechanical ventilation fans, closes fire dampers automatically, and activates pre-discharge audio-visual alarms in protected spaces.

2
Personnel Evacuation & Space Sealing

Verify all crew members evacuated via headcount. Confirm quick-closing valves (QCV) tripped, fuel pumps stopped, and all skylights/doors sealed gas-tight.

3
Open Master Valve First

Open the designated master distribution valve to the space requiring extinction (Engine Room or Cargo Hold). This ensures the discharge line to nozzles is open before high-pressure gas is released into the manifold.

4
Actuate Pilot Release Cylinder

Pull the pilot bottle release lever. High-pressure pilot gas travels down the pilot line to pneumatically open the cutter heads across the required cylinder bank, discharging 85% of CO2 within 2 minutes.

3. Quantity Calculation & the Worked Vessel

For "how much CO2 does your ship carry?" (Q21e), give the percentages, the formula, then your ship's worked example:

VOLUME SETS THE GAS MACHINERY 35 percent CARGO 40 percent WEIGH find leakage
30% Largest Cargo Space Volume
40% Machinery Space (Excl. Casing)
35% Machinery Space (Incl. Casing)
85% / 2 min Discharge Rate Requirement

SOLAS quantity regulations & formulas:

Cargo Holds (30%)

30% Gross Volume Formula:

N = (V_cargo × 0.30) ÷ 0.56 ÷ 45.4
  • Sized for the largest single protected cargo hold
  • Gas delivered selectively via 3-way distribution manifold
  • 0.56 m³/kg is free CO2 volume at 21.1 °C, 1 bar

Machinery Space (40% / 35%)

Casing Area Rule:

Excl: 40% • Incl: 35% ÷ 0.56 ÷ 45.4
  • Use 40% if casing area ≤ 40% of horizontal floor area
  • Use 35% if casing is included in total volume
  • Must discharge ≥ 85% of total required gas in ≤ 2 minutes

Worked Vessel Bank (212 Bottles)

Shipboard Installation:

  • 201 Cylinders: Main Engine Room total flood
  • 7 Cylinders: Dedicated Purifier Room flood
  • 4 Cylinders: Uncommitted spare inventory
  • Actual Test: 107 s total discharge (within 120 s design)
  • Storage: 58 bar @ 21 °C; tare 72–80 kg; gross ~120 kg

4. Weighing & the Maintenance Schedule

For "how do you weigh a bottle?" (Q21f) and "what maintenance?" (Q21g), give the tool, the steps, then the full interval table:

OVERHEAD TRAVELLING TROLLEY / SUSPENSION CROSSBAR FULCRUM PIVOT ± 5° Level GRADUATED SCALE (0 – 220 kg) 118 kg Pull Handle (Level to 90° ± 5°) YOKE CO2 45.4 kg TARE: 74.5 kg TP 250 BAR GROSS: 119.9 kg Strap Loosened ↑ Lifted Clear (≥ 20 mm) CRITICAL ACCEPTANCE CRITERIA • Recharging Limit (−10%): If CO2 content loses > 10% (i.e. > 4.54 kg), the bottle must be sent ashore for refill. • Reading Angle Protocol: Beam pulled down until perpendicular (90°); Reading invalid if inclination exceeds ± 5°.
Figure 3: Mechanical Beam-Scale Assembly for CO2 Cylinder Contents Verification. The cylinder clamping strap is released, the yoke engages the neck flange, and the steelyard arm is balanced horizontally (±5°) clear of the deck. A loss exceeding 10% requires immediate cylinder recharging.
Beam-scale rig with bar, hook, yoke and scale
Reference sketch (course notes): the beam-scale rig — bar, hook, yoke and 0–220 kg scale. Source: Kunjal Shah Part 2 — Fire Fighting Appliances.
Bottle weighing drill in hook-on, hoist and read steps
Reference sketch (course notes): the weighing drill in three figures — hook-on, hoist and read. Source: Kunjal Shah Part 2 — Fire Fighting Appliances.

SOLAS CO2 System Maintenance Ladder:

Interval Inspection / Service Action Test Pressure & Criteria
Weekly Room ventilation run, cylinder clamping tightness, mechanical linkage checks, flexible loop hoses inspected. Bridge notified; 2-person safety buddy system; gas-free check.
Monthly Remote release cabinet door opened; pre-discharge alarm & ventilation trip interlocks verified. Microswitch trips fans and closes fire dampers automatically.
Yearly Pneumatic through-blow of all manifold piping and distribution lines with service air. 25 bar compressed service air; ensures nozzles clear of rust/scale.
2-Yearly 100% cylinder inventory weighed using calibrated mechanical beam-scale or ultrasonic level detector. Recharge mandatory if content loss > 10% (> 4.54 kg).
5-Yearly Manifold spring-loaded safety relief valve bench pressure test; internal valve inspection. 180 bar pop test pressure; seats resealed and class stamped.
10-Yearly Hydrostatic pressure testing of all seamless high-pressure CO2 cylinders (hydraulic stretch test). 250 bar hydraulic test; retested every 5 years after the initial 10-year survey.
15-Yearly Complete distribution pipeline sectional hydraulic pressure testing: manifold to nozzles. 170 bar (manifold), 80 bar (section master valves), 6–7 bar (nozzles line).

5. Engine-Room & Purifier-Room Fire Actions

Knowledge of the system is only half the question — the surveyor then gives you a fire: "E/R on fire — your actions?" Note first that the engine room also has a hypermist system — if you are sure it will extinguish the fire you may operate it with no shutdowns needed; but if the surveyor asks for CO2, explain CO2.

STOP — SEAL — FLOOD STOP fuel + fans SEAL vents + doors FLOOD release CO2

Fire in the engine room — actions in order:

  • On seeing fire anywhere in the engine room, immediately raise the fire alarm from the nearest point by breaking the glass — and if the hammer is missing, remove a safety shoe and strike with its steel toe plate.
  • If the fire type is recognisable and not too big, attack with the proper portable extinguisher.
  • If it cannot be extinguished, immediately run to inform the Chief Engineer and the deck officer or bridge — report location and type of fire.
  • If the main engine is running, slow down and stop it.
  • Before leaving the engine room on orders to release CO2, make sure all accesses are closed properly.
  • Stop the running auxiliary engines and start the emergency generator on load — stopping the auxiliaries also stops ventilation; then close the flaps.
  • All crew except the bridge watchkeeper (or officer/master) muster for headcount, then follow muster-list duties — closing vents, doors, flaps, dampers and quick-closing fuel valves.
  • Start the emergency fire pump for boundary cooling of the engine-room bulkheads, continuously.
  • Operate CO2 from the fire control station; confirm every crew member present, nobody missing.
  • Open the release cabinet with the key — opening it cuts ventilation power and sounds the CO2 release alarm in the engine room.
  • Operate the pilot-cylinder valve and the master valve to release the gas.
  • Continue boundary cooling and check the bulkhead temperatures from time to time.

Fire in the purifier room — actions in order:

  • The purifier room also has hypermist — use it if it will help, with no shutdowns; explain CO2 when the surveyor asks for CO2.
  • Immediately raise the fire alarm by breaking the glass (shoe-steel-toe fall-back as above).
  • Stop the purifier from outside the room with the emergency stop.
  • If the fire type is recognisable and not too big, use the proper portable extinguisher.
  • Close the purifier-room door — do not forget to close it.
  • Immediately run to inform the Chief Engineer and the deck officer or bridge — location and type of fire.
  • Shut purifier-room ventilation from the MSB and shut the flaps.
  • Shut the quick-closing fuel valve for the purifier line only.
  • Carry out boundary cooling for the purifier room.
  • The Chief Engineer releases CO2 from outside the purifier room or from the fire control station; keep up boundary cooling.
Say It in Order

Alarm → muster → headcount → stops → dampers → cooling → evacuate → release. Actions out of order — cooling before stops, release before headcount — fail the question even when every item is named.

6. Purifier Fire Prevention & Closing Drill

The surveyor's last move is "how do you prevent a purifier fire?" — give the six fitted defences, then close with the number drill:

CLEAN — COOL — CONTAIN CLEAN oil mist out COOL bearings fed DRAIN no hot pool

Prevention of purifier fires — six points:

  • All pipes leading to the separator are double-sheathed — an inner-pipe leak drains into the outer pipe instead of spraying over the room.
  • Drip trays below the purifier/separator catch spilled oil so it cannot flow, spread and touch hot material.
  • All pipe flanges and connections are wrapped with anti-spill tape to contain flange leakage.
  • Fixed protection fitted: water-mist and CO2 systems installed in the space.
  • Quick-closing valves and remote stopping of pumps and purifier provided.
  • Fire detection and alarm system provided so quick action can be taken.

Closing number drill — recite cold:

  • Principle: smothering + cooling, O2 below 15%; cat-A ≥ 500 cu m; 85% in 2 min.
  • Bottles: drawn steel, hydro 228 bar, stow ≤ 55 °C at ~52 bar, disc 177 bar at 63 °C, syphon tube against freezing.
  • Room: sole use, ≤ 1 deck down with stair/ladder, 6 changes, outward gas-tight doors, 2.4 m, aft of collision bulkhead.
  • Quantities: 30 / 40 / 35% through V × factor / 0.56 / 45.4; ship carries 212 at 58 bar, 107 s vs 120 s.
  • Upkeep: beam 0–220 kg ± 5°, recharge at 10%; ladder 25 – weigh – 180 – 250 – 170/80/6-7.
Favourite Trap

"Why not release CO2 immediately?" — because men, ventilation and fuel come first: evacuate, headcount, stop air and fuel, seal, cool boundaries — then release. CO2 in a breathing, ventilated space kills men and wastes gas.