Back to Boiler
Auxiliary Machinery & Shipboard Systems

Troubleshooting the Boiler

Boiler faults do not arrive as single readings — they arrive as patterns, where one indication moves first and the rest follow.

20 min read
Advanced
Auxiliary Machinery & Shipboard Systems
Key Principles at a Glance 8 points
  • Confirm the indication is real before anything else — a blocked glass, a failed transmitter or a scanner fooled by hot refractory will make you cause exactly the damage the protection was designed to prevent.
  • Contain the risk first: reduce firing, secure the burner and protect people before investigating.
  • Black smoke means incomplete combustion — the fault is usually atomisation, fuel temperature or air, not the fuel itself.
  • A pulsating flame can extinguish and relight repeatedly, leaving unburnt fuel and producing pressure pulses — investigate promptly.
  • When the two gauge glasses disagree, prove both independently; until they agree the actual level is unknown.
  • High exit gas temperature with normal firing points at the gas path, not the burner — deposit, bypassed gas, or fouled downstream surface.
  • A passing blowdown valve and a feed check valve reverse-leaking both imitate a tube leak; check their individual signatures before condemning a tube.
  • Never defeat an alarm or trip because it is suspected of being faulty — repair it, or remove the boiler from service.

1. The method

Boiler faults do not arrive as single readings. They arrive as patterns — one indication moves first, and the others follow as consequences.

The troubleshooting method follows that structure:

1

Confirm the indication is real, not an instrument fault, by checking it against an independent source.

2

Contain the risk. Reduce firing, secure the burner, protect people, before investigating anything.

3

Compare the related readings. Level, pressure, flow, temperature, and flame move together.

4

Find the cause before adjusting anything.

5

Correct the cause, not the symptom.

6

Prove the boiler is safe before returning to normal load.

7

Record the fault, the action, and the result.

The single most important step is step 1. A gauge glass can be blocked. A transmitter can fail. A scanner can be fooled by hot refractory. Acting on a false reading causes exactly the damage the real protection was designed to prevent.

2. Combustion problems

Boiler burner and air register arrangement
Boiler burner and air register arrangement

The air register splits combustion air into primary and secondary streams, gives them rotation through the swirl vanes, and mixes them with the fuel cone. The primary air carries the flame near the burner; the secondary air completes the combustion in the larger body of the flame. Most combustion faults are a failure of either the atomisation or this mixing.

2.1 Black smoke

What it means: incomplete combustion. Carbon that should have burned has left as soot.

Causes and their checks:

CauseWhy it produces smokeCheck
Poor atomisationLarge droplets cannot burn in the available residence timeBurner tip, swirl plate, orifice, cap nut
Fuel temperature too lowViscosity high, droplets form poorly and burn lateHeater, viscosity control, steam supply to the heater, control valve
Fuel pressure lowInsufficient energy to atomisePump condition, relief valve, filter differential, line restrictions
Insufficient combustion airNot enough oxygen to burn the carbonFan operation, damper position, air register, air path blockage
Air register wrongly setPoor mixing leaves fuel-rich zones that do not burn completelyRegister position against the maker's setting
Burner worn or damagedSpray pattern disturbed; inconsistent droplet sizeBarrel, tip, gaskets, seating in the carrier
Boiler overloadedResidence time reduced below what the droplets needFiring rate against boiler rating; steam demand
Water in the fuelInterrupts the flame locally; poor ignition of dropletsTank drains, purifier operation, filter drains
Blocked or fouled gas pathReduced combustion volume and disturbed aerodynamicsUptake temperature, draught, gas-side condition
Incorrect burner positionFlame sits in the wrong place in the furnaceBurner seating and carrier alignment

Immediate action: reduce firing, correct the cause, confirm clean combustion before increasing the load again.

Consequences if left: MARPOL Annex VI breach and possible detention; soot deposits on gas-side surfaces; rising uptake temperature; increased risk of an uptake fire; wasted fuel.

Pressure-jet burner nozzle assembly
Pressure-jet burner nozzle assembly

The cap, body, orifice plate, and swirler plate are the parts that control atomisation. Erosion of the orifice increases flow for the same pressure and coarsens the spray. Blockage of the swirl holes distorts the pattern. Damage to the cap or body seating causes leakage and dribble. All of these appear as smoke at the funnel before they appear as anything else.

2.2 Orange or smoky flame with high stack temperature

What it means: combustion is finishing late, in the gas path rather than in the furnace.

Causes:

  • Excess fuel for the air supplied.
  • Insufficient air.
  • Fouled heating surfaces reducing heat absorption, so gas leaves hotter.
  • Incorrect burner position, moving the flame into a cooler part of the furnace.

Check: air-fuel ratio, burner condition, gas-side cleanliness, and the burner's position in the carrier.

2.3 Unstable or pulsating flame

What it means: the flame front is not staying in one place. Either the mixture velocity is varying, or the mixture strength is varying.

Causes:

  • Draught fluctuation — fan hunting, damper instability, or a furnace pressure control loop out of tune. The furnace pressure oscillates, and the flame follows it.
  • Air register or damper hunting — the actuator or linkage is moving without a command, or the control loop is unstable.
  • Water or air in the fuel — the fuel supply is not continuous, so the mixture strength varies.
  • Fuel pressure variation — pump wear, a sticking relief valve, or an unstable heater control changing viscosity.
  • Partly blocked burner tip — the spray pattern is asymmetric, so mixing varies around the flame.
  • Furnace pressure control at fault — the set point is wrong, or the transmitter is faulty and the controller is chasing a false value.

Danger: a pulsating flame can extinguish and relight repeatedly. Each extinction leaves unburnt fuel, and the relight can produce a pressure pulse. Investigate promptly.

2.4 Failure to ignite

Work through the ignition sequence in order, because each step depends on the previous one:

1

Purge not complete. The burner management system will not permit ignition. Check airflow proving, fan, dampers, timing.

2

Igniter not proven. Check electrode condition, gap, position, insulation, transformer, and the igniter's own proving circuit.

3

Fuel not reaching the burner. Check the shut-off valve operation, fuel pressure at the burner, filters, and whether the line has been vented of air.

4

Fuel too cold or too viscous. Check the heater and the viscosity control. A cold burner will not light at low fire.

5

Atomising medium missing. Check supply pressure and confirm the line has been drained.

6

Burner assembly wrong. Tip, swirl plate, or orifice fitted incorrectly, or the burner not seated.

7

Air quantity wrong. Too much air at light-off blows the flame away; too little gives a rich mixture that will not ignite.

8

Lockout not reset. The burner management system may require manual reset after a fault.

2.5 Flame failure during running

What it means: a flame existed and then did not.

Causes:

  • Fuel supply interrupted — pump fault, valve movement, filter blockage, or air in the line.
  • Fuel temperature collapse — heater fault or steam supply loss. Viscosity rises, atomisation fails, and the flame goes out.
  • Burner blockage — carbon or debris blocks the tip during running.
  • Airflow or furnace pressure instability — the flame is blown out or destabilised.
  • Scanner fault — the flame is fine but the scanner cannot see it. A dirty lens or a blocked sight tube produces a false flame failure.
  • Flame shape moved — the flame is still burning but has moved out of the scanner's field of view.

The distinction matters: a real flame failure is a combustion problem; a false one is an instrument problem. Either way the burner trips and the furnace is purged, so the immediate consequence is the same, but the repair is different.

3. Water level problems

3.1 Low water level

CauseHow it produces the symptomCheck
Feed pump faultNo flow into the boilerSuction, filters, discharge pressure, standby pump operation
Feed control valve faultValve not opening on demandControl signal, actuator, valve travel, strainer
Feed check valve faultFlow reverse-leaks back down the feed lineLine temperature downstream of the check valve; valve condition
Blocked gauge passageThe glass reads a false low or responds slowlyBlow through both glasses and compare
Level transmitter faultThe controller sees a false high level and does not add waterCompare with direct reading
Tube leakWater leaves through the leakFeedwater flow vs steam flow; leak signs; funnel appearance
Blowdown passingContinuous water loss through a leaking blowdown valveValve condition; drain line temperature
Sudden load changeSwell collapses and the true level is lower than the indicationPost-change level; load history
Feedwater pressure lowValve fully open but insufficient flowPump discharge, system pressure
Hotwell level fallingNo water available to feedHotwell level and the route back from the consumers

Immediate action: confirm the true level, secure firing if genuinely low, do not feed into a possibly overheated boiler unless the procedure allows, find the cause.

3.2 High water level

CauseHowCheck
Feed valve stuck openContinuous feed regardless of levelValve position and command
Controller set point wrongLevel is being held at the wrong valueSet point against the required level
Swell from load increaseVolumetric rise mistaken for a real riseLoad history; level response
FoamingFroth raises the apparent levelChemistry; oil contamination; dissolved solids
Transmitter reading lowController adds water to correct a false lowCompare with the glass
Operator errorValve left open after a manual adjustmentValve position

Consequence: carryover. Water leaves with the steam, taking dissolved salts with it, and deposits them on superheater tubes and turbine blading. It also produces water hammer.

3.3 Level hunting

CauseMechanism
Control tuning wrongThe loop over-corrects, then over-corrects back
Feedwater pressure fluctuationThe valve position no longer produces the expected flow, so the loop keeps correcting
Feed valve sticking or oversizedOversized valve makes small corrections impossible; a sticking valve moves in steps
Impulse line partially blockedThe transmitter sees a delayed or damped signal, so the loop is always working on stale information
Insufficient pressure compensationSteam and water density changes at different loads change the apparent flow and level
Multiple boilers interactingTwo level loops fighting through a common feedwater system
FoamingThe bubble layer makes the level move unpredictably

3.4 Both glasses show different levels

CauseCheck
Blocked steam or water passage on one glassBlow through each glass individually and observe refill behaviour
Wrong valve positionConfirm all three cocks on each glass
Glass or gland leakVisible leakage at the fitting
Glass wrongly mounted or fittedAgainst the maker's arrangement
Prove both glasses independently

Until both agree, the actual level is unknown, and the boiler should be operated conservatively with close attention to the feedwater flow and the steam flow.

Gauge glass mountings — steam, water and drain cocks to check on each glass
Gauge glass mountings — steam, water and drain cocks to check on each glass

When the two glasses disagree, work through the mounting on each glass in turn: steam cock, water cock, drain cock, and the passages into the drum. The blow-through behaviour in Topic 5, section 2.2 tells you which passage is blocked.

4. Steam pressure and temperature problems

4.1 Low steam pressure

CauseMechanism
Insufficient firingThe boiler is not being asked to generate enough
Poor combustionFuel is not being converted to heat efficiently
Fouled heating surfacesHeat is not transferring to the water
Steam leak in the systemSteam is leaving before it reaches the user
Excessive auxiliary demandMore consumers on line than expected
Feedwater problemReduced water in the boiler reduces evaporation
Burner lockout on one of two burnersHalf the expected heat input
Air leakage into the furnaceExcess air is being heated without contributing to combustion
Wrong fuel temperaturePoor atomisation reduces the effective heat release

4.2 High steam pressure

CauseMechanism
Firing not reducing with loadThe pressure controller or its transmitter has failed
Sudden loss of steam demandPressure rises until firing catches up
Main stop valve throttled or closed with the boiler firingNo outlet for the steam
Safety valve not relievingPressure continues to rise past the set point
Pressure controller in manual with a high firing rateOperator has left the plant on manual

4.3 High steam temperature

CauseMechanism
Low steam flow through the superheaterLess cooling for the same heat input
Excessive firing at low loadHeat input out of proportion to steam flow
Attemperator or desuperheater faultThe cooling mechanism has failed
Gas-side bypass or damper in the wrong positionMore heat directed to the superheater
Fouling changing heat absorptionHeat distribution along the gas path has changed
Superheater tube partially blockedReduced flow through some elements, so they overheat locally
Poor water circulationLess heat absorbed elsewhere leaves more for the superheater

4.4 Low steam temperature

CauseMechanism
Attemperator passingCooling water continues to enter when it should not
Superheater fouledDeposits insulate the superheater, reducing heat absorption
Low load with low gas temperatureNot enough heat available to superheat
Carryover wetting the steamWater is being evaporated in the superheater instead of steam being heated
Desuperheater or bypass arrangement in the wrong positionHeat is being deliberately removed

4.5 Wet steam and carryover

Causes:

  • High water level.
  • High dissolved solids, particularly chlorides and sodium salts.
  • High alkalinity.
  • Oil contamination.
  • Sudden load change.
  • Damaged or displaced steam separators.
  • Insufficient blowdown.
  • Mechanical carryover from a damaged internal fitting.

Consequences: turbine blade erosion; superheater tube deposits; water hammer; unstable superheat; corrosion from the dissolved gases carried in the water.

Action: reduce level if high; check chemistry; increase blowdown as permitted; find the oil source if oil is present; inspect separators at the next opportunity if the problem persists with correct chemistry.

5. Water-side problems

SymptomLikely causeMechanismCheck
Hard scale on tubesHardness ingress, treatment ineffectiveCalcium and magnesium salts precipitate on hot surfacesChemistry trend; make-up water quality; dosing system
Soft sludge accumulationInsufficient bottom blowdownPrecipitated solids settle in low-velocity areasBlowdown record; bottom blowdown practice
PittingDissolved oxygen not controlledLocal oxygen attack breaks the oxide filmDeaerator performance; scavenger dose; reserve level
General corrosionLow pH, carbon dioxideThe whole surface is attacked by acidpH and alkalinity results; condensate quality
Caustic attackHigh caustic alkalinity concentrating under deposits or in crevicesIntercrystalline cracking; metal becomes brittleCaustic alkalinity result; deposit survey
Chloride attackSeawater ingressChloride and magnesium chloride produce hydrochloric acidChloride result; condenser tightness; make-up water
Oil in the boilerContamination from a heating coil or lubricating systemOil coats tubes, promotes overheating and foamingOil test; heater coil condition; coagulant dosing
Rising chlorideSeawater ingressCondenser leak, primed evaporator, or untreated make-upCompare chloride against feedwater and condensate results
FoamingHigh solids, oil, high levelStable froth forms on the surfaceChemistry, level, oil test
Water hammer in the economiserEconomiser steamingTrapped steam collapses and water slugs accelerateFeedwater flow and temperature; recirculation arrangement
Corrosion fatigueCyclic stress on a corroded surfaceCracks initiate at pits or grooves and propagate under stressDeposit and crack survey at overhaul
DezincificationSelective removal of zinc from brassFittings become weak and porousCondition of brass fittings and tube plates
Economiser elements — check here first for water hammer and steaming
Economiser elements — check here first for water hammer and steaming

Water hammer in the economiser means this surface is steaming instead of heating water: trapped steam collapses and the water slug hammers the tubes. Check feedwater flow and temperature and the recirculation arrangement before blaming the steam line.

6. Gas-side problems

6.1 High flue-gas or uptake temperature

CauseMechanism
Soot or deposit on surfacesThe deposit insulates, so less heat is absorbed
Damaged or missing bafflesGas short-circuits past the surfaces it should cross
Incorrect air-fuel ratioEither excess air raising the gas volume, or poor combustion raising the exit temperature
OverloadMore gas flow than the surfaces were designed for at that temperature
Poor circulationWater-side heat absorption is reduced
Wrong damper position or gas bypassGas is routed away from the surfaces
Air heater or economiser fouledDownstream of the fouling, gas stays hotter

Action: reduce load if necessary; soot blow if the deposit is soft soot; investigate baffles at the next opportunity; check air-fuel ratio.

Soot blowers and control dampers — gas bypass and fouling points
Soot blowers and control dampers — gas bypass and fouling points
Rotary air heater — downstream fouling keeps gas hot
Rotary air heater — downstream fouling keeps gas hot

High exit temperature with normal firing points at the gas path, not the burner: deposit insulating the surfaces, a damper or baffle letting gas bypass the surfaces, or the air heater / economiser fouled so gas stays hot downstream. Compare temperatures before and after each surface to localise the fouling.

6.2 High furnace pressure

CauseMechanism
Blocked or restricted uptakeGas cannot leave as fast as it is produced
Damper problemA damper is closed or partly closed when it should be open
Fan or draught control faultThe balance between supply and extraction is wrong
Excessive firing or air supplyMore gas being generated than the path can carry
Fouled gas pathIncreased resistance to flow
Soot-blower seal failureGas escaping or air entering through the wall box
Never open the furnace doors to investigate high furnace pressure

Risk: hot gas and flame escaping into the casing space and the engine room, plus the potential for casing damage. The pressure is being held in by the closed doors, and opening them releases it.

6.3 Rising gas-side differential pressure

  • Soot or hard deposit build-up.
  • Damaged baffles creating local restrictions.
  • Refractory fragments lodged in the gas path.
  • A soot blower left in the gas path.

6.4 Signs of a developing soot or uptake fire

  • Uptake temperature rising rapidly, not gradually.
  • Local hot spots on the casing, uptake, or stack.
  • Sparks or flame visible at the stack.
  • Burning smell.

Action: reduce or stop firing; do not soot blow into the fire; apply the approved smothering method; boundary cool; inspect before restart.

7. Mechanical and pressure-part problems

7.1 Tube leak

Evidence:

  • Falling water level with the feedwater valve fully open.
  • Feedwater flow persistently exceeding steam flow.
  • Falling steam pressure and output at constant firing.
  • Wet or white appearance at the funnel.
  • Steam or water escaping from the casing, handholes, or around fittings.
  • A leak noise inside the furnace, changing with load.

Distinguish from:

  • A passing blowdown valve — check the blowdown valve and its drain line temperature.
  • A feed check valve reverse-leaking — check the temperature of the feed line downstream of the check valve.
  • Normal swings in level from load change.

Action: secure and isolate as instructed; cool naturally; inspect when depressurised and cool; identify the failure mechanism before repair.

7.2 Refractory damage

CauseMechanism
Rapid heating or coolingThermal stress cracks and spalls the refractory
Flame impingementLocal overheating of the quarl or furnace floor
Fuel contaminationAsh and impurities react with the refractory surface
Poor anchorageRefractory falls away from its fixings
VibrationCracking and spalling at restrained edges
Water or steam leakageThermal shock and erosion at the leak point

Consequence: flame instability, poor combustion, hot spots on the casing, and gas leakage through the damaged area.

7.3 Support and expansion problems

  • Restricted expansion causing distortion, cracking, or over-stressed nozzles.
  • Corroded or loose holding-down arrangements allowing movement.
  • Pipe expansion loads transferred to boiler nozzles because the pipe supports are wrong.
  • Slide and roller supports seized, so the boiler cannot move as designed.

7.4 Casing and insulation corrosion

Usually found under the insulation and around mountings, manholes, handholes, and drains, where a small leak has been running. The insulation holds moisture against the steel, and the corrosion continues unseen.

Check for staining and for insulation that is damp, soft, or detached. Remove insulation locally, clean, inspect, treat, and re-protect.

8. Instrument problems versus real problems

An abnormal reading is either a real condition or a failed measurement. The two require completely different responses, and acting on the wrong one is dangerous.

ReadingSuspect the instrument whenSuspect a real fault when
Low drum levelOne glass reads low and the other is normal; the transmitter signal is erraticBoth glasses low; feedwater flow is high and the level still falls
High drum levelThe remote indication is high but the glasses are normalBoth glasses high; steam appears wet; carryover signs
High steam pressureLocal gauge stuck; other pressure indications disagreeSafety valve lifts; other gauges agree; firing rate is high
Low steam pressureOne transmitter suspect; no change in firing or levelFiring rate is high for the output; steam leak signs
High steam temperatureSingle probe suspect; no change in flue gas or flameFlue gas temperature, load, and attemperator position all agree
No flame signalScanner lens dirty; sight tube blocked; but the furnace is clearly lit through the sight portFuel and air are present but the furnace is dark
Low feedwater flowPositioner or transmitter faulty; pump discharge pressure normalPump pressure low; level actually falling
High flue-gas temperatureProbe or thermocouple faulty; other points normalMultiple gas temperatures high; draught and fan load changed

The procedure when an instrument is suspected:

1

Find an independent indication of the same quantity.

2

If the independent indication is normal, treat the suspect instrument as faulty and repair or replace it.

3

If no independent indication exists, operate conservatively until the measurement can be confirmed.

4

Never defeat an alarm or trip because it is suspected of being faulty — repair it, or remove the boiler from service.

9. Fault patterns worth memorising

Black smoke + high uptake temperature + high fan current. Fouling with poor combustion. Check burner and air-fuel ratio first; the fouling is a consequence.

Falling level + high feedwater flow + falling steam pressure. Loss of water from the system. Distinguish between a tube leak, a passing blowdown, and a feed check valve fault by checking their individual signatures.

Rising level + wet steam + unstable superheat. Carryover. Check the level first, then the chemistry, then the separators.

Level falling when steam demand rises, then tripping. Single-element level control responding to swell. The fix is in the control scheme, not in the boiler.

Steam temperature rising at low load. Insufficient steam flow through the superheater. Check the attemperator, the firing rate, and the load.

Furnace pressure rising + uptake temperature rising + fan current rising. Gas path resistance increasing. Check the uptake, dampers, soot blowers, and gas-side cleanliness.

Flame failure with a good flame visible. Scanner or sight tube problem. Clean and prove the scanner.

Safety valve lifting at correct pressure with normal firing. Pressure controller or transmitter fault, or a sudden demand loss. Check the controller before assuming the valve is wrong.

10. Quick reference

BLACK SMOKE             atomisation, fuel temperature, air, burner, register, load
FLAME UNSTABLE          draught, fuel pressure, water in fuel, burner tip, register
NO FLAME AT LIGHT-OFF   purge, igniter, fuel supply, viscosity, atomising medium
FLAME FAILS RUNNING     fuel interruption, temperature collapse, burner blockage,
                        scanner fault, draught instability

LOW LEVEL               feed pump, feed valve, check valve, leak, blowdown passing,
                        gauge blockage, transmitter, shrink after swell
HIGH LEVEL              feed valve stuck, set point, swell, foaming, transmitter
LEVEL HUNTING           tuning, feedwater pressure, valve size or sticking,
                        impulse line, density compensation
GLASSES DISAGREE        blocked steam or water passage, valve position

LOW PRESSURE            firing, combustion, fouling, leak, demand, feedwater
HIGH PRESSURE           controller, demand loss, stop valve closed, safety valve
HIGH TEMPERATURE        low steam flow, overfiring, attemperator, dampers, fouling
WET STEAM               level, solids, oil, load change, separators, blowdown

HIGH UPTAKE TEMP        soot, baffles, air-fuel ratio, overload, circulation
HIGH FURNACE PRESSURE   uptake, dampers, fan balance, firing, gas path fouling

TUBE LEAK               falling level, rising feed flow, wet exhaust, leak noise
REFRACTORY DAMAGE       rapid heating, flame impingement, contamination, anchorage

11. Recording the fault

For every fault, record:

  • Time of first observation and of each action.
  • The indication that moved first.
  • What the other related indications were doing.
  • What you checked and what you found.
  • What you did, and the result.
  • Who was informed.
  • What remains to be done — for example, an inspection to be carried out at the next opportunity.

This record is what turns a series of unrelated breakdowns into a maintenance history, and it is what the next engineer uses to understand what happened.