Fire Safety

Topic 5 of 7

Back to Fire Safety
Tools

Ship Fire Main & Emergency Fire Pump System

Ship fire main layout, main and emergency fire pumps, hoses, nozzles, hydrant pressures, isolating, relief and drain valves with SOLAS figures.

Published by ChartandKeel Updated

1. Fire Main Purpose & General Principles

The fire main is a system consisting of sea-water inlet(s), suction piping, fire pumps and a distributed piping system supplying fire hydrants, hoses and nozzles located throughout the vessel. Its purpose is to provide a readily available source of water to any point throughout the vessel which can be used to combat a fire, and it is considered the backbone of the fire-fighting systems on board.

Through the fire main the firefighter gets a reliable and versatile system offering several methods of attack: water can be supplied as a straight stream (jet) for deep-seated fires, as a spray for combustible-liquid fires where cooling and minimum agitation is desired, or as a means to protect personnel where cooling is the primary effect desired.

  • 2.6 kJ/g — Heat Absorption to Steam
  • 1600× — Steam Volume Expansion
  • 2 × 12 m — Mandatory Jet Throw
  • 3.5 kg/cm² — Top Hydrant Working Pressure

Extinguishing capabilities of water:

Sensible & Latent Heat Absorption

Heating water from ambient to 100 °C and converting it into steam absorbs 2.6 kJ/g (1117 BTU/lb). This massive thermal sink drops the combustion zone temperature below the fuel's auto-ignition point.

1600× Smothering Steam Blanket

Upon vaporisation at atmospheric pressure, 1 m³ of liquid water expands into 1600 m³ of steam vapour, rapidly displacing ambient oxygen around the flame envelope and suffocating the combustion.

Versatile Jet & Spray Delivery

Applied as a solid high-velocity jet for deep-seated Class-A embers, a wide-angle mist fog for cooling Class-B oil spills without fuel splashing, and water curtains for boundary cooling of adjacent bulkheads.

Distributed Ring Architecture

Supplied by at least 2 independent main pumps plus 1 emergency fire pump outside machinery spaces, serving distributed deck hydrants equipped with instantaneous couplings and dual-purpose nozzles.

How to answer in viva. For "what is the purpose of the fire main?", say: backbone of firefighting — sea inlet to hydrants everywhere — cooling plus 1600× steam smothering at 2.6 kJ/g — applied as jet, spray and boundary cooling.

Ship fire main: normal and emergency supply Two main fire pumps inside the machinery-space boundary draw from the main sea suction and deliver through separate checks to an engine-room branch and the deck fire main. An isolating valve accessible outside the boundary separates that branch from the deck header. An emergency pump with its own sea suction and independent drive lies outside the boundary and connects through a check to the deck side of the isolating valve. Its suction and discharge do not pass through the machinery space. Hydrant valves are connected to hoses and nozzles. Teal arrows show the emergency supply route; closing the isolating valve separates damaged machinery-space pipework. Machinery space Space boundary Sea suction Main pump 1Main pump 2 Checks ER branch Isolating valveOutside access Check Emergency pumpIndependent drive Own sea suction Deck fire-main distribution Hydrants + hoses
Figure 1: Ship fire main: normal and emergency supply — The main pumps feed the engine-room branch directly and the deck main through an externally accessible isolating valve. The emergency pump has its own suction and independent drive outside the machinery space, and joins the deck side of that valve. Isolation separates damaged engine-room pipework from the emergency-fed distribution.
Hand-drawn fire main with pumps, isolating valves and hydrants
Reference sketch: the fire main on one page — pumps, deck/emergency/engine-room isolators and hydrant branches.

2. Emergency Fire Pump Regulation

Apart from the main fire pumps, an emergency fire pump is provided for emergencies such as CO2 flooding or main fire pumps dysfunctional. For "give the emergency-pump regulation", give position, drive, suction and figures together:

Main fails — backup runs: Place outside E/R; Drive own power; Throw two jets.

Emergency Fire Pump Statutory Requirements (SOLAS Ch. II-2 Reg. 10 & FSS Code):

The emergency fire pump is the vessel's ultimate firefighting lifeline should a major fire, total blackout, or flooding knock out the main engine room fire pumps. Surveyors and PSC inspectors verify its operational readiness, priming ability, and discharge pressure during almost every inspection.

Cargo Ship Fire Main and Emergency Fire Pump statutory arrangement
Figure 14.1: Cargo ship fire main and emergency fire pump statutory layout. The independent diesel-driven emergency pump (suction head ≤ 4.5–6 m) is isolated from the machinery space by an isolating stop valve located outside the engine room.
  • 40% — Main Pumps Total Capacity
  • ≥ 25 m³/h — Min Cargo ≥2000 GT & Pax
  • ≥ 15 m³/h — Min Cargo <2000 GT
  • ≥ 0.27 N/mm² — Min Hydrant Working Pressure

Statutory Location & Access

Must be situated outside Category-A machinery spaces (typically installed in the steering gear compartment, shaft tunnel, forward pump room, or emergency generator flat). Access must not be compromised by smoke, fire, or heat from the engine room. If access requires passing through the engine room, it must be protected by an airlock with two self-closing A-60 steel fire doors.

Prime Mover & Cold Starting

Driven by an independent compression-ignition diesel engine OR a dedicated electric motor powered exclusively from the Emergency Switchboard (ESB). The diesel engine must be capable of starting from cold down to 0 °C by hand cranking or power starting, and down to −15 °C with preheating aids (glow plugs/jacket heaters). Two independent energy sources must be provided (e.g. primary electric battery starter plus secondary manual hydraulic or spring accumulator starter).

Fuel Oil Supply & Endurance

The diesel engine must have an independent service fuel tank containing sufficient fuel with flash point ≥ 43 °C to run the pump at full load for at least 3 hours. A reserve stock of fuel stored outside the machinery space must ensure full operation for a further 15 hours (total 18 hours endurance).

Suction Lift & Priming Mechanism

Must have an independent sea chest. The total suction head must not exceed 4.5 metres (statutory maximum 6 metres) at the vessel's lightest seagoing ballast waterline under any condition of list (15°) or trim (10°). Must be fitted with an independent automatic priming device (water-ring liquid pump, compressed air ejector, or vacuum primer). If suction piping traverses machinery spaces, it must feature ≥ 11 mm wall thickness, all-welded joints without flanges, and A-60 fire insulation.

Discharge Pressure & Jet Delivery

When discharging through any two adjacent hydrants fitted with standard 12 mm (or 16 mm / 19 mm) nozzles, the pump must maintain a minimum working pressure of 0.27 N/mm² (2.8 kg/cm² / 2.7 bar) at the third hydrant, throwing two powerful, coherent water jets with a horizontal throw of not less than 12 metres each.

External Isolating Valve

A screw-down non-return or stop fire main isolating valve must be positioned on the fire main pipework outside the machinery space in an easily accessible position. Shutting this valve isolates the engine-room fire main from the deck fire main, ensuring that a pipe rupture inside a burning engine room cannot depressurize the deck hydrants supplied by the emergency fire pump.

Memory hook for viva. Recite: 40% — 25 — 15 — 0.27 N/mm² — 2 × 12 m: 40% of main capacity, 25 or 15 m³/h minimum, maintaining 0.27 N/mm² while throwing two 12-metre jets — from outside the machinery space with independent sea suction and 3+15 h fuel reserve.

3. Hoses, Nozzles & Hydrant Pressures

Hoses and nozzles carry the water from the hydrant to the fire — surveyors test construction, stowage, lengths, couplings and pressures closely.

  • 18 m / 64 mm — Hose Length & Diameter
  • 15 / 20 / 25 m — ER / Deck / Wide Decks
  • 17 / 24 bar — Working / Test Pressure
  • 12 / 16 / 19 mm — Dual Nozzle Orifices

Fire Hose Construction & Testing

Made from synthetic woven textiles, lined with smooth synthetic rubber and coated with PVC. Highly resistant to rot, mildew, marine climate, and hydrocarbons. Tested annually to 50% above working pressure (17 bar WP → 24 bar TP).

Dual-Purpose Nozzle Function

Approved type incorporating solid jet, wide-angle spray, and complete shut-off in one twist assembly. Orifices: 12 mm, 16 mm, and 19 mm (accommodation restricted strictly to 12 mm). Delivers average ≥ 5 L/m²/min.

Two-Jet Coverage Mandate

Hydrant positions must allow at least two jets of water from separate hydrants (one from a single length of hose) to reach any normally accessible area on board, including cargo spaces when empty.

SOLAS Hydrant Working Pressures

  • With 2 main pumps running: 3.5 kg/cm² (50 psi) at top two hydrants.
  • Passenger Ships: ≥4000 GT: 0.40 N/mm² | <4000 GT: 0.30 N/mm²
  • Cargo Ships: ≥6000 GT: 0.27 N/mm² | <6000 GT: 0.25 N/mm².
Dual-purpose nozzle: jet, spray and shut-off Three longitudinal sections of a representative adjustable sleeve-and-deflector nozzle. Water enters from the hose coupling and passes around a spider-supported central spindle. With the sleeve extended beyond the fixed deflector, the outlet gathers water into a jet. With the sleeve retracted clear of the cone, water strikes the deflector and spreads outward as spray. In the shut position, the sleeve seat contacts the tapered cone and closes the annular water passage. Seals between the body and sleeve prevent leakage at the sliding interface. The geometry illustrates one design, not all dual-purpose nozzles. Hose couplingAdjustable sleeve JET Gatheredaxial stream Water passageCentral spindle SPRAY Deflectedoutward spray Fixed cone / deflector SHUT Seat contacts cone Passage closed Body-to-sleeve seals
Figure 2: Dual-purpose nozzle: jet, spray and shut-off — This representative sleeve-and-deflector design varies the outlet geometry around a fixed central cone. An extended sleeve gathers the water into a jet; a retracted sleeve lets the deflector spread it outward as spray. In the shut position the sleeve seat contacts the cone. Actual nozzle mechanisms and adjustment sequences vary.
Fire hose reel — always charged and ready
Reference photo: the hose reel — always charged and ready.
Fire hose box
Reference photo: the hose box.
Fire hose and couplings — check washers and lugs during rounds
Reference photo: hose and couplings — check washers and lugs during rounds.
Fire hose spanners kept at hose stations
Reference photo: the spanners kept at hose stations.
Fire hydrant outlet coupling
Reference photo: the hydrant outlet coupling.

4. Relief, Drain & Isolating Valves

Valves keep the main alive when part of the ship is on fire, and protect the pumps and the main itself.

Isolate — drain — relief: Isolate cut section; Drain frost clear; Relief lift at set.

Spring-Loaded Pressure Relief Valve

Fitted on pump discharge headers. Automatically lifts if pumps exceed pipework design pressure. Crucially protects ship pipework and hydrants from excessive pressure during shore supply connection in dry dock.

Low-Point Anti-Freezing Drain Valves

Fitted at all low points along weather deck and exposed fire mains. Drains standing water when the system is idle, preventing catastrophic pipe ruptures caused by water freezing in sub-zero polar latitudes.

Machinery Space Isolating Valve

Fitted in an easily accessible and tenable position outside the engine room. When closed, keeps the entire deck and accommodation fire main pressurised via the emergency pump even if the engine room is flooded or ablaze.

Tanker Poop Front & 40 m Deck Valves

On oil/chemical tankers: one screw-down isolation valve sits in a protected position at the poop front bulkhead, plus additional valves along the tank deck at intervals of not more than 40 metres to isolate ruptured sections.

Tanker oral-exam rule. On tankers the isolating valve sits at the poop front in a protected position with tank-deck isolations at not more than 40 m intervals — quote both figures together.

5. Main Diameter & Fire-Main Sketch Points

For "draw the fire-main system" (Q24) and "what is the diameter of the fire main?" (Q24d), give the sizing rule and the sketch contents:

  • 2 Pumps — Simultaneous Maximum Discharge
  • 140 m³/h — Cargo Ship Main Capacity
  • ≤ 40 m — Tanker Deck Valve Spacing
  • Anti-Clockwise — Hydrant Valve Opening

Main Diameter Sizing Rule

Pipe diameter is dimensioned for effective distribution of maximum combined discharge from two main fire pumps operating simultaneously. On cargo ships, diameter need only be sufficient to carry 140 m³/h.

Sketch Checklist: What to Draw

  1. Open sea chests → 2 main pumps with NR valves
  2. Relief valve overboard
  3. Machinery space isolating valve
  4. Emergency pump outside ER
  5. Poop front & 40 m deck valves
  6. Hydrants, hoses & dual nozzles
  7. International shore connection.
Tanker deck fire main: loops and isolation A representative longitudinal tanker deck arrangement. The machinery-space supply feeds an accommodation and engine-room branch, separated from the cargo-deck main by a protected isolating valve at the accommodation front. The supported deck pipe includes a continuous U-shaped expansion loop with no straight bypass. Two sectional isolating valves divide deck hydrant branches. Closing a sectional valve interrupts supply beyond it unless another approved supply route is available; spacing and protection are ship-specific. Accommodation / ER Cargo deck — representative layout From fire pumpsSeparate accommodation / ER branch Protected isolation Expansion loop Sectional isolating valves Valved hydrants + hoses Pipe supports
Figure 3: Tanker deck fire main: loops and isolation — The supported cargo-deck main incorporates an expansion loop and sectional isolating valves serving valved hydrants. Protected isolation at the accommodation front separates the deck main from accommodation and machinery-space pipework. Isolating a damaged section can interrupt downstream supply; continued coverage depends on the ship’s actual pump connections and routing.

6. Q24 Oral-Exam Recap & Figure Table

For "draw the fire-main system" (Q24) plus sub-questions Q24a–Q24e, answer in this order — purpose, pumps, emergency pump, hoses and nozzles, pressures, valves, diameter:

Q24 main-system rapid answers:

  • Composition: sea-water inlets, suction piping, 2 fire-main pumps, distributed main, hydrants, hoses and nozzles — the backbone giving water at every point.
  • Attack modes: jet for deep-seated fires, spray for liquid fires with minimum agitation, personnel shielding and boundary cooling.
  • Water figures: cooling to 100 °C then steam at 1600× expansion — 2.6 kJ/g (1117 BTU/lb) — cooling plus smothering.
  • Pumps: 2 main pumps, FSS-Code capacity, remote start, sea valves always open; performance two 12 m jets from the farthest hydrants.
  • Use limits: first choice for Type-A fires; on Class-B only after all other modes fail.

Q24a–Q24e rapid answers:

  • Q24a isolation function: separates the machinery-space pump section from the rest so all other hydrants stay supplied by the second or emergency pump; fitted outside in a tenable position, on tankers poop-front protected plus 40 m tank-deck valves, screw-down type.
  • Q24b pump regulation: emergency pump outside M/C at embarkation-deck level, diesel with battery plus hand-crank, primed, 40% with 25 / 15 m³/h minima, two 12 m jets.
  • Q24c hose and nozzle regulation: synthetic 18 m / 64 mm, deployed 15 / 20 / 25 m, annual 50%-over test (17 / 24 bar); dual jet+spray with shut-off, 12 / 16 / 19 mm, 12 mm in accommodation, 5 L/m²/min.
  • Q24d diameter: serves two pumps together — 140 m³/h on cargo ships.
  • Q24e relief: yes — against over-design pressure and against shore-supply damage in dry dock; drains guard against icing.
ItemSOLAS Requirement / Technical FigureOral-Exam Key Note
Main Fire Pumps2 independent pumps, remote start from Bridge/ECRSea suctions kept permanently open
Emergency Fire Pump40% of main capacity; ≥ 25 m³/h (or 15 m³/h <2000 GT)Outside machinery space at embarkation level
Mandatory Jet ThrowsTwo 12 m jets from farthest hydrantsOne jet on single hose length reaches any area
Hose Lengths15 m ER; 20 m decks; 25 m wide decks >30 m beamSynthetic textile, rubber-lined, PVC-coated
Hose Proof Pressures17 bar working pressure; 24 bar annual testAnnual 50% overpressure hydraulic test
Nozzle Types & SizesDual-purpose jet + spray + shut-off; 12, 16, 19 mmAccommodation limited strictly to 12 mm; ≥ 5 L/m²/min
Top Hydrant Pressure3.5 kg/cm² (50 psi) with 2 pumps runningPax: 0.40/0.30 N/mm²; Cargo: 0.27/0.25 N/mm²
Isolating ValvesOutside tenable position; Tankers ≤ 40 m deck intervalsPreserves deck main if ER flooded or on fire
Main DiameterTwo pumps combined; min 140 m³/h on cargo shipsEnsures full simultaneous delivery without choke

Trap answers. "Which way does a hydrant valve open?" — anti-clockwise. "Can a hose be removed with pumps running?" — yes, each hydrant has its own valve. "What stops overpressure?" — the relief valve.

Figure 4: Fire-main relief and isolating valvesReused direct spring-loaded relief cutaway in the lifted state, with an illustrative easing lever mechanically linked to the disc spindle. A separate threaded rising-stem globe stop valve is seated closed; pressure reaches its inlet but no through-flow is shown.Fire-main valve cutawaysRelief · LIFTEDStop · CLOSEDEasing leverSpringSeatInletOutletHandwheelThreadPackingDisc / seatFire mainIsolated
Figure 4: Fire main valve details. Left: Spring-loaded pressure relief valve with hand easing lever, protecting pipes from overpressure during fire pump operation or shore connection in drydock. Right: Heavy-duty screw-down isolating stop valve with rising spindle (opens anti-clockwise), providing bubble-tight segregation between machinery spaces and deck sections.

7. Shore Coupling, Hydrant Fittings & Hose Boxes

For "what fittings sit between the main and the hose?", describe the chain from hydrant valve to nozzle exactly as the notes list it:

  • 178 mm — ISC Flange Outer Diameter
  • 64 mm — ISC Inside Bore Diameter
  • 132 mm — Bolt Circle PCD
  • 4 × 19 mm — Slotted Bolt Holes

Hydrant Body & Valve

Every hydrant features an anti-clockwise opening control valve. Positioned so any single hose can be engaged, disengaged, or removed while fire pumps run continuously under full head pressure.

Fire-Hose Box Equipment

Stowed conspicuously adjacent to the hydrant. Contains: one approved synthetic fire hose (flaked or rolled), one dual-purpose jet/spray nozzle, and the dedicated coupling spanner wrench.

International Shore Connection (ISC)

Standardized universal flange carried on board. Enables the ship to couple instantly to any municipal or shipyard fire tender worldwide during port layover or dry-docking.

Fastener Kit Specification

Must be stored with the ISC flange: 4 steel bolts of 16 mm diameter × 50 mm length, 8 flat washers, and 1 full-face non-asbestos elastomeric gasket rated for 10.5 bar.

Sketch labels to recite in viva. Label the drawing: hydrant → anti-clockwise valve → flange → snap-in hose → dual nozzle, plus the hose box, spanner and international shore coupling — every item the Q24 sketch plates show.

Figure 5: International shore connection and complete fittingsFour-slot flange face drawn to FSS dimensions: 178 mm outside, 64 mm bore, 132 mm pitch circle and 19 mm open slots. Side section shows a flat face, minimum 14.5 mm flange and a permanently attached illustrative ship coupling. Complete kit depicts four 16 by 50 mm bolts, four nuts, eight washers and one compatible gasket.International shore connection · FSS dimensionsFlange faceSide sectionØ64 mmØ178 mmPCD Ø132 mm4 × Ø19 slotsShip couplingFlatface≥14.5 mmComplete connection kit4 bolts · Ø16 × 50 mm8 washers4 nutsGasket
Figure 5: SOLAS International Shore Connection (ISC) technical engineering drawing with standard dimensions: 178 mm outer diameter, 64 mm inner bore, 132 mm bolt circle (PCD), 14.5 mm minimum flange thickness, and 4 slotted holes of 19 mm diameter. Kept complete in a dedicated box with 4 bolts (16 × 50 mm), 8 washers, and 1 gasket.

Standards & sources referenced

  • SOLAS: International standards for the safety of life at sea.
  • FSS Code: Technical requirements for fire safety systems.
  • Conventions index