Fire Fighting - General — Most Asked Questions

28 questions asked about fire fighting - general across the General and Fn 3 papers, heaviest first. 3 of them are must-master.

28 questions 0 ticked
  1. 1 deck fire fighting system on chemical tankers?

    Must master Theory asked 108 times · across 15 examiner banks General

    Answer

    Chemical tankers carry a fixed deck foam system sized well above crude-oil practice because chemical fires are hotter and harder to kill.

    • Chemical tankers: foam capacity the largest of entire cargo deck at 2.0 litre/m2/min, or 20 litre/m2/min over the single largest tank.
    • Oil tankers for comparison: 0.6 litre/m2/min over the whole deck or 6.0 litre/m2/min over the largest tank — roughly a third of chemical-tanker figures.
    • System parts: seawater supply pumps, foam-liquid storage, proportioning device and deck distribution with monitors and applicators.
    • It must knock down spill fires, stop unignited spill igniting, and fight fires in ruptured tanks.

    Surveyor follow-up: why does a chemical tanker need three times the foam rate of a crude carrier?

    Full theory: Deck Foam & Inert Gas (IG) Systems on Tankers
  2. 2 Purifier room fire fighting system?

    Must master Theory asked 15 times · across 10 examiner banks General

    Answer

    The purifier room is a high-fire-risk machinery space: hot oil under pressure plus mist means fixed local protection, detection and quick isolation.

    • Purifier and cargo-pump spaces sit inside the machinery-space fire-protection envelope with foam, water-mist coverage and portable backup.
    • Fixed local application (hyper-mist/water spray) covers the purifier flat: fine mist from pressure-drop nozzles smothers oil fires without flooding electrics.
    • Detection and control: flame/smoke detection over the flat, high- and low-water alarms on the mist unit, detector supervision.
    • Isolation on fire: stop purifier feed pumps, trip ventilation, close quick-closing fuel valves remotely — then fight the fire, never feed it.

    Surveyor follow-up: purifier high-temperature alarm with mist in the room — keep running to finish separation or stop first?

    Full theory: Ship Sprinkler & Hypermist (Water Mist) Systems
  3. 3 Emg fire pump

    Must master Theory asked 19 times · across 6 examiner banks General

    Answer

    The emergency fire pump sits outside the engine room so one fire cannot kill every pump, and must feed at least two hoses anywhere on board.

    • Capacity not less than 40% of the main fire pumps’ total, and never below 25 m³/h.
    • Pressure: cargo ships 1000–6000 GT at least 2.6 bar, above 6000 GT at least 2.8 bar.
    • Location outside the engine room — typically forward, steering flat or shaft tunnel — easily accessible, with its own suction (total suction head within 4.5 m under all trim and list).
    • Drive independent: electric from the emergency generator, or diesel hand-started with two battery sets (six starts in 30 minutes, two within 10), fuel tanks full for 3 hours plus 15 hours reserve.

    Surveyor follow-up: main fire pump and emergency pump both run — how do you prove the two jets reach the poop and the forecastle together?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  4. 4 Firefighting arrangement system on deck

    Revise Theory asked 4 times · across 2 examiner banks · 2 wordings merged Fn 3

    Also asked: “Firefighting system on board”

    Answer

    Deck fire cover means two jets anywhere: hydrants near protected-space access, hoses coupled fast, mains that never freeze.

    • Hydrants sited so two jets from different hydrants — one on a single hose length — reach any crew space.
    • Pipes and hydrants coupled easily with isolating valves splitting the machinery-space section.
    • Relief valves guard pump pressure above design; drains empty the line against icing in sub-zero trades.
    • Nozzles, hoses and international coupling kept ready with the main pressurised throughout.

    Surveyor follow-up: one hydrant reaches everywhere alone — compliant or not, and why two jets?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  5. 5 What is semi portable extinguisher

    Revise Theory asked 4 times · across 2 examiner banks · 2 wordings merged Fn 3

    Also asked: “What is semiportable type extinguisher”

    Answer

    Semi-portables are wheeled big brothers of hand extinguishers: 50–150 kg units needing two crew for monitors and manifolds.

    • Wheeled foam, powder and CO2 units parked at engine-room, boiler and purifier platforms.
    • Powder sizes near 50, 70 and 150 kg running about three minutes on outside CO2 expulsion.
    • Controllable nozzles stretch reach where hand bottles fall short.
    • Two-person drill: one on the hose, one on the valves — never single-handed against a running fire.

    Surveyor follow-up: hand bottle or semi-portable for a purifier-flat fire — which one, and who mans it?

    Full theory: Classes of Fire & Portable Fire Extinguishers on Ships
  6. 6 How will you know that priming arrangement for emergency fire pump is working satisf

    Revise Fault finding asked 3 times · across 3 examiner banks General

    Answer

    Prove priming by water, not hope: priming tank full, casing vented solid, suction open, pressure rising on start.

    • Priming-water tank full with vacuum-pump check valve proved on its line.
    • Suction fully open with discharge shut and casing vent cracked until solid water shows.
    • Start and open discharge gradually watching suction and discharge pressures with amps steady.
    • Ballast-condition suction lift proved separately — loaded-draft success never proves ballast lift.

    Surveyor follow-up: pressure hunting with the tank full — air leak, foot valve or suction lift, and what proves it?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  7. 7 Fire fighting in cargo space

    Revise Theory asked 4 times · across 2 examiner banks Fn 3

    Answer

    Fight cargo fires from outside first: cool boundaries, starve vents, then flood the space with gas and hold it sealed.

    • Cool boundaries all round with hoses so the fire cannot migrate through steel into the next hold.
    • Vent skilfully for a cool-air approach path, never letting fire cut the escape route.
    • Flood with CO₂ to 35–50% and hold concentration with hatches sealed and fans stopped.
    • Re-enter only trained, equipped and permitted with lifelines and breathing sets after time and tests prove it.

    Surveyor follow-up: boundary hot with smoke easing after gas release — re-enter, re-flood or keep cooling, and what decides?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  8. 8 Deck fire fighting for bulk

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

  9. 9 Difference between valve and hydrant

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    The valve controls the fire main; the hydrant is the outlet a hose connects to — the tap and the spigot.

    • Isolation valves on the fire main shut a section for repair or to stop a damaged main feeding the fire.
    • Hydrants are the deck outlets with hose couplings, sized so two jets from different hydrants reach any crew space.
    • Each hydrant has its own valve so a single outlet can be isolated without shutting the whole main.
    • The international shore connection is the ship’s other inlet, sized to marry the shore main in any port.

    Surveyor follow-up: deck fire main isolated at one valve with two hydrants left live — sound isolation or a fire risk?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  10. 10 Emcy fire pump solas requirements

    Revise Theory asked 2 times · across 2 examiner banks · 2 wordings merged General

    Also asked: “Emcgy fire pump requirements”

    Answer

    The emergency fire pump is independent insurance: its own power, its own fuel and enough capacity for two jets.

    • Capacity at least 40% of the main fire pump and never less than 25 m³/h, so two independent jets can be manned.
    • At least two jets must be delivered, not both from the same hydrant, with one hose length between them.
    • Installed outside the engine room, usually forward of the collision bulkhead, at the steering gear flat or in the tunnel.
    • Diesel-driven with start by hand or battery, fuel for 3 hours running plus a reserve tank for 15 hours further.

    Surveyor follow-up: emergency pump proved with only one hydrant in the test — does that satisfy the two-jet rule?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  11. 11 Fire fighting booklet

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    The fire control plan is the ship’s fire-fighting manual in picture form, stowed where the bridge and the crew can reach it.

    • Stowed in a marked container on the bridge, in the fire control station and in the engine control room.
    • Shows portable and semi-portable extinguisher positions, EEBD locations and quantities, and the fixed systems.
    • Gives the detection and alarm arrangement, the ventilation system, and the number and location of fire hydrants.
    • Also shows lifeboat and liferaft positions, means of escape, and fire-main and fuel-line isolation points.

    Surveyor follow-up: plan on the bridge missing the engine control room copy — which station does the surveyor ask for?

    Full theory: Fire Control Plan, Muster List & Flooding Response
  12. 12 Fire fighting equipment

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    Fire-fighting gear is fixed and portable: fire mains, hydrants, fixed systems and extinguishers chosen by the class of fire.

    • Fixed: fire mains with hydrants, emergency and main pumps, water mist, foam, CO₂ and sprinkler systems as fitted.
    • Portable: water, foam, dry powder and CO₂ extinguishers sized and sited for the spaces they protect.
    • Semi-portable: wheeled units for engine rooms and galleys, able to be brought to the fire rather than to it.
    • Supporting gear counts too: fire blankets, buckets, EEBDs, breathing sets and the fire control plan itself.

    Surveyor follow-up: galley with only portable CO₂ and no fixed system — adequate for a galley fire or not?

    Full theory: Classes of Fire & Portable Fire Extinguishers on Ships
  13. 13 Fire fighting in e/r

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    Engine-room fires are fought by restriction: alarm, isolate fuel, cut the air supply, cool boundaries, then the fixed system.

    • Sound the fire alarm, inform bridge and chief engineer, and state the size, location and whether machinery must stop.
    • Never use water on oil or electrical fires; restrict with remote quick-closing valves on the fuel supply.
    • Stop the engine-room blowers to cut fresh air but keep the exhaust fans running to clear smoke.
    • For severe fires evacuate, start the emergency generator and emergency fire pump, release the fixed system, and cool from outside.

    Surveyor follow-up: fuel fire in the engine room with the fire main already charged — isolate first, or fight first?

    Full theory: Fire Control Plan, Muster List & Flooding Response
  14. 14 Fire fighting on deck n working

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    Deck fires are boundary problems: cool what is behind you, isolate fuel and ventilation, and never let the fire find the accommodation.

    • Close the space below and cool the boundary while the deck party attacks with the correct medium for the fuel.
    • Shut ventilation and isolate the fuel or cargo transfer — a deck fire spreads on air and vapour, not on steel.
    • Move the ship to put the fire away from the accommodation and keep a clear escape route and a water curtain ready.
    • Account for the crew and muster them, and do not re-enter the space until it is cool and the atmosphere tested.

    Surveyor follow-up: deck fire with the accommodation bulkhead warm and no boundary cooling — which comes first?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  15. 15 Fire fighting requirements for engine room

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    Engine rooms carry detection, alarm, fixed extinguishing, fire main coverage and the means to shut the space down safely.

    • Fixed detection and alarm in periodically unattended and automatically controlled machinery spaces, with the panel outside.
    • Fixed extinguishing sized for the space, with remote shutdown of fuel, ventilation and machinery on activation.
    • Fire main coverage from at least two hydrants reachable by one hose length, plus the emergency fire pump standing by.
    • Portable and semi-portable extinguishers placed for the class of fuel, with an emergency fire plan at the station.

    Surveyor follow-up: engine room with a single hydrant reachable from the rest of the ship — does the two-hose rule hold?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  16. 16 Fire fighting system installed

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

  17. 17 Firefighting system on deck of your ship

    Revise Your ship asked 2 times · across 2 examiner banks Fn 3

    Answer

    The deck system is foam and water: monitors, fire main, hydrants and the portable extinguishers that finish what the monitors start.

    • A deck foam system blankets burning oil from monitors controlled at a station clear of the cargo area.
    • The fire main and hydrants give cooling and boundary work, with foam monitors laying the blanket on the oil itself.
    • Portable dry powder and CO₂ cover the fringe — the fire main cools, the foam blankets, the extinguisher finishes.
    • Quote the ship’s actual arrangement: monitors, the foam ratio, the fire main pump and the extinguishers in the fire plan.

    Surveyor follow-up: deck fire with the foam supply isolated at the control station — who opens it, and is that in the plan?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  18. 18 Fixed foam fire fighting arrangemnet for deck?

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    The deck foam system is a loop: foam tank, foam pump, proportioner, foam monitors and the control station clear of the cargo.

    • The foam tank holds the concentrate, with a P/V valve on the vent so the tank breathes without losing the blanket.
    • The foam pump draws concentrate and a diaphragm valve/proportioner makes it to the required mix with seawater.
    • Foam monitors discharge the blanket onto the deck, and the fire main is there for cooling and boundary work alongside.
    • The control station sits away from the cargo area, and the whole deck is covered inside 5 minutes with at least 20 minutes supply.

    Surveyor follow-up: deck foam tested with the proportioner valve closed and the discharge still clear — is the foam the right grade?

    Full theory: Deck Foam & Inert Gas (IG) Systems on Tankers
  19. 19 How to check efficiency of dcp portable extinguisher

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    A dry powder extinguisher is checked by weighing it and proving it fires: charge weight, pressure, and a discharge at the maker’s figures.

    • Weigh the extinguisher and compare with the full charge weight on the body — that is how loss is found, not by eye.
    • Check the pressure gauge on a stored-pressure set, and the CO₂ cartridge where fitted, replacing a spent cartridge.
    • Discharge it at least yearly and check the nozzle for a sharp crackling discharge at the set pressure.
    • Check the safety pin, the relief hole, the cap and the body: a body of solid drawn steel, zinc coated inside and out.

    Surveyor follow-up: extinguisher a kilogram light with a good gauge reading — is it leaked, partly discharged, or just not weighed?

    Full theory: Classes of Fire & Portable Fire Extinguishers on Ships
  20. 20 How to test emergency fire pump

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    Start it, run it on the fire main and prove it delivers two independent jets — a test that never pressurises nothing.

    • Start from the emergency generator or by hand, and let it run long enough to warm and prove the prime.
    • Deliver through the fire main to two hydrants not in line with each other, and read the pressure and flow.
    • Check the running hours, fuel for 3 hours plus 15 hours reserve, and the condition of the starting batteries.
    • Record the test with pressures, timing and any defect — an untested emergency pump is the pump nobody trusts.

    Surveyor follow-up: pump started weekly but the last two-hour delivery test was a year ago — running proof or delivery proof?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  21. 21 If main fire pump not working then how to supply water

    Revise Fault finding asked 2 times · across 2 examiner banks Fn 3

    Answer

    The emergency fire pump takes over on its own line, with the emergency generator and the shore connection as the layers behind it.

    • The emergency fire pump is fed from a separate suction, so it runs when the main pump and the sea chest line are out.
    • The emergency generator starts automatically to give it power, so a total main board loss does not stop the fire main.
    • In port the international shore connection can supply the fire main directly, and portable monitors can be fed from it.
    • If all of that is lost, the ship is a total loss by definition — so the emergency layers are tested, not assumed.

    Surveyor follow-up: main pump failed with the emergency pump proved running but no power — what has actually stopped the water?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  22. 22 On main deck fire line which devices are there?

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    The deck fire main carries hydrants, isolation valves, branch connections and the international shore connection.

    • Hydrants spaced so two jets from different hydrants reach any crew space on one hose length.
    • Isolation valves at intervals and at every accommodation and engine-room entrance, all operable from outside.
    • The international shore connection for shore supply in any port, with its gasket, bolts and coupling ready.
    • Drain cocks at low points for draining in frost, and relief valves where the main is long or the ship high.

    Surveyor follow-up: main deck hydrant with no isolation valve aft of it — a maintenance point or a fire risk first?

    Full theory: Ship Fire Main & Emergency Fire Pump System
  23. 23 Portable and semi portable

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

  24. 24 Semi portable dcp and foam

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

  25. 25 Something recording fire line on deck he asked

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    The surveyor was after the fire-main diagram: the run of the main, the hydrants, the isolation valves and the foam connection points.

    • Show the fire main run along the deck with every hydrant, valve and branch to the accommodation and machinery spaces.
    • Mark the emergency fire pump and its separate suction, and the international shore connection at its actual position.
    • Mark the foam system take-off and the monitors, and the portable extinguisher stations along the same route.
    • Carry the diagram on the fire control plan and in the fire party’s hands — the surveyor reads the route, not the symbol.

    Surveyor follow-up: fire main diagram showing a valve with no label and a hydrant behind the foam manifold — what is missing?

    Full theory: Fire Control Plan, Muster List & Flooding Response
  26. 26 What is class k fire?which ext to extinguish it?what is fixed fire fighting arrangements for galley fire?

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    Class K is cooking oil: smother it with wet chemical, never water, and the galley carries a fixed system over the range.

    • Class K covers cooking oils and fats, which burn at temperatures no dry powder or CO₂ will truly extinguish.
    • Wet chemical extinguisher saponifies the burning oil into a soapy foam that smothers it — water on it causes a violent boil-over.
    • Galleys carry a fixed extinguishing system over the range with dual thermostats, a power cut-off and an alarm in the galley.
    • Fire blankets at the door, clean ducts and filters on schedule, and burners proved off after cooking complete the picture.

    Surveyor follow-up: galley oil fire with a dry powder extinguisher open in the locker — which agent, and can you reach it?

    Full theory: Classes of Fire & Portable Fire Extinguishers on Ships
  27. 27 What type of foam inside semiportable ext

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    Semi-portable foam extinguishers carry low-expansion foam — protein, fluoroprotein or a film-forming blend, depending on the fuel.

    • Foam extinguishers discharge a blanket, so the agent is low-expansion foam for oil and flammable liquid fires.
    • Protein foam burns back slowly and resists re-ignition; fluoroprotein and film-forming blends are faster to spread and cut fuel vapour.
    • The concentrate is premixed with water by the proportioner in the extinguisher, which is why the nozzle gives a foam and not a jet.
    • Check the label for the grade and the expansion ratio, and prove it discharges as foam rather than solution.

    Surveyor follow-up: semi-portable discharging a clear jet at the fire — is the concentrate, the proportioner or the nozzle?

    Full theory: Classes of Fire & Portable Fire Extinguishers on Ships
  28. 28 Which ship sailed. I told vlcc. Asked firefighting systems onboard. Then asked about hypermist system. How it works. Sensors for getting system activated. How to test sensors

    Revise Your ship asked 2 times · across 2 examiner banks Fn 3

    Answer

    On a VLCC, hypermist is a zoned water mist for the accommodation and machinery spaces, activated by detectors and proved with clean water.

    • Two detectors must agree before release: the panel zones the fire and signals the hypermist control panel.
    • The control panel starts the plunger pump and opens that zone’s solenoid valve — about 200 litres per minute at 70 bar.
    • Nozzles pass 12–20 litres per minute at 50 bar, making a cooling fog that smothers without the water load of a deluge.
    • Test the sensors with the approved test agent, then discharge each zone with clean water and prove the flow and pressure alarms.

    Surveyor follow-up: zone proved with the pump running but no flow alarm — is the flow switch, the strainer or the nozzle?

    Full theory: Ship Sprinkler & Hypermist (Water Mist) Systems

Source: 123 written papers and surveyor oral banks, 24,613 entries, merged into 17,210 topics. Ticks are stored on this device only.