Sounding & Level Measurement — Most Asked Questions

7 questions asked about sounding & level measurement across the General and Fn 6 and Fn 3 papers, heaviest first.

7 questions 0 ticked
  1. 1 How will you check boiler low low level alarm?

    High priority Fault finding asked 11 times · across 8 examiner banks · 2 wordings merged General

    Also asked: “How to test boiler low level alarm”

    Answer

    Prove the low and low-low alarms for real by dropping the water level in the chamber — never by just pressing the test button.

    • Test on every watch or daily: drain/blow down the float chamber so the floats actually fall with the level.
    • Low-water alarm must sound first; at low-low the burner must cut out and lock out — confirm both, not just the bell.
    • On a water-tube boiler a lost level turns dangerous in minutes from high evaporation rate and small reserve, so class demands the protection.
    • After the test blow through the gauge glass, refill the chamber and reset — log time, level and burner response.

    Surveyor follow-up: alarm sounds on test but the burner keeps firing — what has failed?

    Full theory: Boiler Safety Devices and Emergency Response
  2. 2 Piston ring calibration?

    Revise Theory asked 4 times · across 3 examiner banks Fn 6

    Answer

    Calibrate rings by groove and gap: feeler top and bottom against the data-plate figure with butt gap proved in the liner.

    • Read vertical clearance top plus bottom with feelers; the total must sit inside the plate figure.
    • Sudden wear jumps mean water through the cooler, dead cylinder oil or abrasive fuel and air.
    • Proving the ring free in its groove matters more than polishing it — stuck rings pump blow-past.
    • Butt gap proved square in the unworn liner band per maker figure before fitting.

    Surveyor follow-up: one unit high exhaust with low compression — rings, valves or timing, and what do you measure first?

    Full theory: Cylinder Liner Wear, Calibration & Cold Corrosion
  3. 3 Calibration of o2 analyzer

    Revise Theory asked 3 times · across 3 examiner banks · 2 wordings merged General

    Also asked: “Oxygen analyser calibration”

    Answer

    Calibrate the O₂ analyser dead-steady: nitrogen for zero, dry air for span, two minutes to settle each time.

    • Zero on nitrogen at the 0–1% range with flow set, trimming the zero knob to a true zero reading.
    • Span on dry air through silica gel, waiting two minutes to equilibrium, trimming span to 21% O₂.
    • A cold cell reads nothing — warm it first; 21% with sample gas flowing means blocked pipe, broken cell or meter fault.
    • Log zero and span drift each watch; recalibrate after filter, pipe or cell work before trusting the bridge reading.

    Surveyor follow-up: analyser stuck on 21% with flue gas applied — calibrate, warm up or open the sample line first?

    Full theory: Instruments & Safety Systems
  4. 4 liner calibration in details

    Revise Theory asked 3 times · across 2 examiner banks · 3 wordings merged Fn 6

    Also asked: “How liner calibration is done?”, “How to take liner calibration”

    Answer

    Liner calibration maps wear against hours: gauge each cylinder fore-aft and athwart at fixed levels, record on the template.

    • Gauge with an inside micrometer at top, middle and bottom of stroke, fore-aft and port-starboard each.
    • Record cylinder number, date fitted, total hours and hours since last gauging on the measurement template.
    • Compare against original bore for wear rate, ovality and taper — scavenge-port and top-ring zones wear fastest.
    • Rising rate with steady hours condemns oil feed, fuel sulphur match or air filtration before the liner does.

    Surveyor follow-up: one cylinder oval with the rest round and hours equal — gauging error, lubrication or alignment?

    Full theory: Cylinder Liner Wear, Calibration & Cold Corrosion
  5. 5 Air pipe and sounding pipe regulation

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    Air pipes breathe the tank and sounding pipes measure it: both are placed by rule, at the right height, and closed against fire.

    • Air pipes go opposite the filling pipe and at the highest point, led above the bulkhead deck or to open deck for oil tanks.
    • The height is not less than about 760 mm on the freeboard deck and 450 mm on the superstructure deck.
    • Sounding pipes are as straight as possible, bore not less than 32 mm, and 65 mm through a refrigerated compartment.
    • Striking plates of adequate size and thickness go under open-ended sounding pipes, with the cover self-closing where it must be.

    Surveyor follow-up: sounding pipe with no striking plate and a 20 mm bore in a reefer compartment — which rule is broken first?

    Full theory: Ship Pipelines — Seawater, Bilge, Ballast & Fuel Systems
  6. 6 How to calibrate gas detector ( by span gas

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    A detector is proved on two gases: zero on nitrogen or fresh air, span on a known gas, and a bump test between.

    • Zero on nitrogen or clean air with the flow set, adjusting the zero knob to a true zero reading.
    • Span on a certified cylinder of known concentration, allowing the reading to settle, and trimming the span control to match.
    • Between calibrations, a bump test with known gas proves it is still reading — the single check that catches a failed sensor.
    • Record the cylinder concentration and date, because a span check against an unknown gas proves nothing.

    Surveyor follow-up: detector passing the bump test but failing span — the sensor, the cylinder or the sample line?

    Full theory: Instruments & Safety Systems
  7. 7 Procedure fo calibrating gas detector

    Revise Theory asked 2 times · across 2 examiner banks Fn 3

    Answer

    Calibrate in order: clean, flow, zero, span, bump — and never with the cell cold or the sample line blocked.

    • The analyser will read falsely if the meter circuit resistance is high, the cell defective or broken, or the pipe blocked.
    • Zero first on nitrogen or fresh air, then span on the certified gas, reading the certificate value rather than a nominal one.
    • The cell will not operate when cold — allow it to reach working temperature before trusting any reading.
    • Finish with a bump test, and log the gases, concentrations and dates against the instrument register.

    Surveyor follow-up: detector reading 21% on flue gas with the sample line proved clear — is it the cell, the meter circuit or a short?

    Full theory: Instruments & Safety Systems

Source: 123 written papers and surveyor oral banks, 24,613 entries, merged into 17,210 topics. Ticks are stored on this device only.